[COLOR=rgba(0, 0, 0, 0.701961)]Just rewiring a 3 storey house that's going to be student lets, communal kitchen lounge bathrooms etc[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]I have worked out the following diversity and demand [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Emergency lights 6a x 0.66 = 2.64a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Smoke alarm 6a x0.66 = 2.64a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]4 light circuits 4 x 6a x 0.66 = 10.56a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]4 ring mains 32a + (3 x 32 x40% = 38.4a) = 70.4a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]That all totals 86.24a [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Dilemma I have is adding electric cookers and electric radiators [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Customer ideally wants 2 stand alone electric cookers but I've worked out each cooker assuming 40a would equal 29.16a if he had 2 it would be 58.32a [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Then he wants 500w convector heaters either 7 or 15 of them spilt over 3 floors in total 15 would bring 7kw and need to be on a 32a fuse and if he went for 7 it would be 3.5kw and need a 16a fuse, apply diversity and that would add 21a or 13a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Questions I have are[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]1. if he had the electric rads could I put 3 radial circuits into one 32a fuse [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]2. As it stands without cookers or rads it's would be[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]86.24a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]115a with one cooker[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]144a with 2 cookers[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]157a with 2 cookers and 7 rads[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]165a with 2 cookers and 15 rads[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Which would be acceptable, my old old lecturer stated if it exceeds 100a it'll just blow main fuse so don't worry
Also found someone using the add up all themcb values and times by .40 anyone else used this or know if it's ok?
cheers
[/COLOR]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Just rewiring a 3 storey house that's going to be student lets, communal kitchen lounge bathrooms etc[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]I have worked out the following diversity and demand [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Emergency lights 6a x 0.66 = 2.64a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Smoke alarm 6a x0.66 = 2.64a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]4 light circuits 4 x 6a x 0.66 = 10.56a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]4 ring mains 32a + (3 x 32 x40% = 38.4a) = 70.4a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]That all totals 86.24a [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Dilemma I have is adding electric cookers and electric radiators [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Customer ideally wants 2 stand alone electric cookers but I've worked out each cooker assuming 40a would equal 29.16a if he had 2 it would be 58.32a [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Then he wants 500w convector heaters either 7 or 15 of them spilt over 3 floors in total 15 would bring 7kw and need to be on a 32a fuse and if he went for 7 it would be 3.5kw and need a 16a fuse, apply diversity and that would add 21a or 13a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Questions I have are[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]1. if he had the electric rads could I put 3 radial circuits into one 32a fuse [/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]2. As it stands without cookers or rads it's would be[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]86.24a[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]115a with one cooker[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]144a with 2 cookers[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]157a with 2 cookers and 7 rads[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]165a with 2 cookers and 15 rads[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]
[/COLOR]
[COLOR=rgba(0, 0, 0, 0.701961)]Which would be acceptable, my old old lecturer stated if it exceeds 100a it'll just blow main fuse so don't worry
Also found someone using the add up all themcb values and times by .40 anyone else used this or know if it's ok?
cheers
[/COLOR]