G

getwiredin

I have a job to install a new 3 phase DB to supply 9 showers in a care home, it is an old installation and the main switch is only rated at 100a. how do i apply diversity to this to see if the existing mains would be adequate, thanks
 
Finding out how many care staff they have working in the morning might give you an idea on how many showers will get used together as i don't think in care homes they can shower alone,
just a bit of info i picked up from homes i work in.
 
Yep trev, as far as i know.
So would be 100% of the largest, 100% of the next largest & 25% of all others.
 
Last edited by a moderator:
I have a job to install a new 3 phase DB to supply 9 showers in a care home, it is an old installation and the main switch is only rated at 100a. how do i apply diversity to this to see if the existing mains would be adequate, thanks

Do the same calculation as for single phase and times it by three. The most important part of this job is keeping the phases as near balanced as possible. You are very unlikely to pull all 300a at anyone time anyway. I have an HMO with 4 x 8kW showers and it has not had a problem since rewired 6 years ago. If yours does tip it over the edge with 9, then you may have to install some sort of relay set up so only so many showers can be on at a time.

Calculation,

Add all breaker values up, i.e 6+6+16+16+32+40 and so on, then multiply the the total by 0.4.

Cheers.........Howard
 
Last edited by a moderator:
I only use the OSG diversity calc when I do not know what the use will be.

As you know intended use, I would explain that with the current set up you can run X at once, is that enough or would you like me to up the wires for X cost.

The water pressure idea is a good one too.
 

Reply to help with diversity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
514
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
805

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top