So a friend of mine has a new build (2020) typical new build lashed in. Hes getting an electric car soon however fitting a charger will be a pain in the backside as the meter cupboard is in passage on the side of the house the fuse board is fed by a sub main and is in the toilet under the stairs which is right in the middle of the house and its a semi detached. Top floor is all fitted flooring so no access that way. Behind the fuseboard is a fully fitted kitchen.
Only way it can be done is in the meter cupboard as the passageway is so tight that you'd never get the bins or anything through it if you fit an enclosure on the wall
My plan would be the fit a 7-8 module board in the meter cupboard and getting rid of the KMF switch feeding the house fuseboard
have the tails in to a 100A isolator then an SPD /SPDMCB if needed then dp rcbo for the car charger circuit then a 63a dp mcb for the house this at the end so that the neutral is on the lhs so no need to cut the busbar
Only problem is finding the parts all from the same manufacturer anybody had any experience of this?
Only way it can be done is in the meter cupboard as the passageway is so tight that you'd never get the bins or anything through it if you fit an enclosure on the wall
My plan would be the fit a 7-8 module board in the meter cupboard and getting rid of the KMF switch feeding the house fuseboard
have the tails in to a 100A isolator then an SPD /SPDMCB if needed then dp rcbo for the car charger circuit then a 63a dp mcb for the house this at the end so that the neutral is on the lhs so no need to cut the busbar
Only problem is finding the parts all from the same manufacturer anybody had any experience of this?