hi can anyone help me with zs
when testing zs using my metrel eurotest meter with a rcd . i canot get a correct reading . i have tryed the meter on diffrent settings but still cannot get it right. i have to get zs by caculation .when doing the test the rcd will trip out
 
hi, if your getting the results by calculation then all you need is a low ohm meter for R1 + R2 then do a loop test on your mains? i think?

when you say cant get a correct reading do you mean its tripping the rcd?

ps..glad i bought a fluke!!

you could always get some insulated leads with croc clips or summat and link out the rcd for the test?? used to do this a while back before getting a descent tester.
 
Last edited:
hi can anyone help me with zs
when testing zs using my metrel eurotest meter with a rcd . i canot get a correct reading . i have tryed the meter on diffrent settings but still cannot get it right. i have to get zs by caculation .when doing the test the rcd will trip out
:)i have got a metrel installtest ,have you tried setting it to no trip.;)
 
i set it to no trip and it gives me the zs but it takes a while and the reading is allways slightly higher than the calculation method.
 
thanks paul i set the meter to non trip to but the readings are a way out are you putting the meter on loop then on to rs(rcd10ma) to do the test
 
hi can anyone help me with zs
when testing zs using my metrel eurotest meter with a rcd . i canot get a correct reading . i have tryed the meter on diffrent settings but still cannot get it right. i have to get zs by caculation .when doing the test the rcd will trip out

Just bought one of these (MI3100 Eurotest Easi) a few weeks back and have been checking it in the same RCD protected socket on our kitchen ring. With the 'trip-lock' selected it's been throwing up readings over 5 or 6 tests between 0.49ohms to 0.54 when I've just tried it again now. Seems to work a treat
same with the ramp test, consistent within +/- a few tenths of a mS. Can't ask more than that. My opinion will change markedly the first time it starts to play up but no trouble so far.

Chews through its battery pack though.
 
Last edited by a moderator:
no .on my meter i set it to no trip which is next to the l-n loop and l-e loop buttons,if im testing a 30mA rcd i set it to 30mA ,it is allways going to be slightly less accurate because it uses less current to do the test in order not to trip the rcd.
 

Reply to help with finding zs with rcd in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
633
  • Question
Great, then I am a bit bemused why you posted your original question. You need to stop doing any work that you cannot properly test, safety is...
Replies
12
Views
1K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top