Hi
Regarding the Generic schedule of test results and form filler version
there is a line on the generic form in the OSG or BS&7671 that says equipment vulnerable to a particular test eg Rcds /flourescents/alarms electronic equipment susceptible to damage from IR tests etc
and also there is a remarks box were you can put vulnerable at the side of the particular circuit
On the formfill version there isnt no line to fill in like this or a remarks box
I am using this cert for my elecsa assessment and need to know if this would be a problem
As in Gn3 it says there should be a diagram /chart or Tables which has this info on
and for simple installations like a domestic as this is a schedule of test resuts with this info on is considered acceptable
page 19 Gn3 2.3.10 - 13
this should have the following info
10. the type and composition of circuits , including points of utilisation, number and size of conductors ad type of cable including method installation
11. the method used for basic and fault protection and where appropriate, the coditions required for ADS
12. the info necessarry for the identification of each device performing the functions of protection, isolation and switching and its location
13. ANY CIRCUIT OR EQUIPMENT VULNERABLE TO A PARTICULAR TEST
should i add a additional sheet with this info on
any advice or info regarding this would be grateful
cheers
Regarding the Generic schedule of test results and form filler version
there is a line on the generic form in the OSG or BS&7671 that says equipment vulnerable to a particular test eg Rcds /flourescents/alarms electronic equipment susceptible to damage from IR tests etc
and also there is a remarks box were you can put vulnerable at the side of the particular circuit
On the formfill version there isnt no line to fill in like this or a remarks box
I am using this cert for my elecsa assessment and need to know if this would be a problem
As in Gn3 it says there should be a diagram /chart or Tables which has this info on
and for simple installations like a domestic as this is a schedule of test resuts with this info on is considered acceptable
page 19 Gn3 2.3.10 - 13
this should have the following info
10. the type and composition of circuits , including points of utilisation, number and size of conductors ad type of cable including method installation
11. the method used for basic and fault protection and where appropriate, the coditions required for ADS
12. the info necessarry for the identification of each device performing the functions of protection, isolation and switching and its location
13. ANY CIRCUIT OR EQUIPMENT VULNERABLE TO A PARTICULAR TEST
should i add a additional sheet with this info on
any advice or info regarding this would be grateful
cheers