hi im doing a install and the outside walls are insulated with kingspan. There is 20mm gap between the kingspan and the plasterboard. Do i wire the install with conduit drops and metal boxes or is it ok to keep the cables in the 20mm gap. its just a ring main circuit.

Thanks
Matthew
 
Either or mate, whichever you prefer. Presume circuits has RCD protection.

If there run between the board and the king span then you may have to apply correction factors
 
Have a look at Tables 4AC, Number 3 Ref method A & 4D5 (Red Book)

Looks like 20mm conduit in the gap would be best to keep the 20A ccc , assuming you're using 2.5mm T&E.
 
yip 2.5 T&E. also there will be a 6mm T&E for the cooker. its a conservatory been built onto the kitchen. so i'm rewiring the kitchen ring main and the cooker is moved. I thought I would ask you guys as I had an argument with the guy I work as he think it only needs conduit when it passes through the kingspan. I thought it had to be put in conduit.
 
your argument would be that if the cable were to be just dropped behind the board, it would not be supported.
 
sounds ok to drop it behind the plasterboard as long as it is in the prescribed cables zones and RCD protected, if it were having to pass through any kingspan then yes, use conduit, as the foam of the kingspan can have a chemical reaction with the PVC of the cable and cause the insulation to deterioate
 

Reply to Help with kingspan in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
988
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
922
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top