I am looking help with some equations that could come up in my 2391 exam ,is there any body out there that could explain to me from start to finish how I calculate voltage drop.
 
Voltage drop = (mV/A/mtr) x Ib x L /1000

(mV/A/mtr) – mV drop per amp per mtr Found in BS7671/OSG

Ib – Design Current

L – Length of cable run in meters
 
.... as above and if it's a three phase circuit (distribution etc). Then adjust the table values by dividing by square root of 3 and include adjusted reactance figure as well (add the two together). Finally you may need to adjust the resistance (but not reactance) for temperature (depending on what table you are using).
 

Reply to help with my 2391- equations? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

S
The coding part is all down to experience and knowing whether something is right or wrong. Remember some pics have no faults.
Replies
2
Views
265
  • Question
Correction: Ignore that last bit, I got confused. The OCPD will still trip in time at the sum of the currents.
Replies
3
Views
580

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top