andrewsbabu

Hello every one

I hired a BT engineer to install a 20A power socket in the garage to run a table saw that needs 16A power supply. After installation of the20A type B MCB, it trips when the saw is started. The saw has a 3 hp motor.

The engineer has gone away and will contact me later. Can anyone help/advice as to what could be the problem.

Many thanks
Andrew.
 
basically when your appliance starts up it pulls more current to get it going than it does in normal operation.
As above for this you need to install a C20 MCB, the "C" denotes that the MCB will tolerate higher currents to get over the start up spike but would trip for prolonged exposure to current over its rated capacity.

LOL - Ask the BT engineer if he also does boilers?
 
Last edited by a moderator:
they must have electricians i no that in the street exchanges they have heaters and sockets in them

If so he will have known that a C breaker is required once he realised what his customer spec was :)
If this was a new circuit did he also give you the certificates required to meet the requirements of the law?
 
While the Type B/C MCB mixup is probably the cause, is there not also a risk that the MCB is tripping because of a fault?

Could the electricians on the forum indicate what tests the BT Engineer should carry out to determine that the motor and its connection is not faulty?
 
I'm not being funny but i thought that the 'BT engineer' is also an electrician. The standard tests should have already been done, R1+R2, insulation resistance, Ze, polarity etc.
 
yea i have plenty of times, but i dont need to get a 3 yr city & Guilds course to do it, as well as insurance and part p registration etc etc lol. im gonna ask the carpet fitter to fit my new CU next week.

And let this be a lesson to all who cut corners! Get the right person for the right job in the first place and save urself the hassle of sorting out all the crap that comes with it! You do realise that ur house insurance will be null and void now without a cert too on the new cct if it ever catches fire!!
 

Reply to Help with new socket installation in Garage. in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Why would you want to fuse them? The RCD should now be a type A plus it is likely you could upgrade the protective device to 20A. What protective...
Replies
3
Views
1K
I have been well informed by your replies. Totally confident going forward now. Extension lead would present a hazard if left in (semi)...
Replies
14
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks