A quick brain dump: Guessing you may need to factor in hire of a lift of some sort (and possibly training?) depending on the venue's ceiling heights.
You may need to come up with a labelling scheme for the accessories, so factor in the cost for that when reviewing for inspection quote (should already have been done and regularly tested (and kept with alarm paper work), but not always available!).
Note accessory identification on form. For maintained, visual check for illumination of sign. Then for circuit under test, isolate and check lamps are on. If lamp not on .. note to check both lamp and battery condition in addition to the usual checks (visual, cpc continuity, etc) for that accessory. Worth taking safety glasses/portable vac/waste bag with you (and don't swallow any of the flies!).
Depends if it's out of hours or in use during inspection (I'd guess the latter, so one circuit at a time (even if you have additional help)). If it's going to be in use (particularly if it's something like a cinema) then try to get an idea of the availability of each section of the complex.
Make it clear whether your contract covers rectification or just reporting of problems. A carefully worded contract covering extra time costs (outside of your control) should be considered (section/room not available when previously agreed that it would be). You may want to have the discussion about one off inspection versus ongoing inspection/maintenance contract as well.