Generic title as since I'm going through the book I might have more than one question (which I have so far).

So, first question. Can somebody explain

559.5.1:

At each fixed lighting point one of the following shall be used for the termination of the wiring system:

(i)...
(ii)...
(iii)...
(iv)...
(v) A suitable socket outlet to BS 1363-2, BS 546 or BS EN 60309-2

And why you might install a BS 1363-2 at a lighting point - I think BS 546 is the 2amp socket that will be installed in a pub window or something, but when would you use a BS 1363-2?

Thanks,
 
Perhaps where the fixed lighting circuit doesn't change, but the lights might. Think: exhibitions in galleries, where each different art installation might want different lanterns.
 
Last edited:
433.3.1 (i)

"A device for protection against overload need not be provided: for a conductor situated on the load side of the point where a reduction occurs in the value of current carrying capacity, where the conductor is effectively protected against overload by a protective device installed on the supply side of that point"

Just trying to grasp how IET word things still, is this the regulation that permits me to wire the first half of a lighting circuit in 2.5mm and the second half of the circuit in 1.5mm so long as the protective device (for example the MCB at the CU) is rated for the 1.5mm cable (so let's say a 6A MCB).

Am I getting the hang of this, or have a just made up a load of bull? Not wiring anything like this, just trying to translate to a scenario where it would be used.
 
433.3.1 (i)

"A device for protection against overload need not be provided: for a conductor situated on the load side of the point where a reduction occurs in the value of current carrying capacity, where the conductor is effectively protected against overload by a protective device installed on the supply side of that point"

Just trying to grasp how IET word things still, is this the regulation that permits me to wire the first half of a lighting circuit in 2.5mm and the second half of the circuit in 1.5mm so long as the protective device (for example the MCB at the CU) is rated for the 1.5mm cable (so let's say a 6A MCB).

Am I getting the hang of this, or have a just made up a load of bull? Not wiring anything like this, just trying to translate to a scenario where it would be used.
you are correct.
 
Thanks Tel. Another one, 542.2.6:

"A metallic pipe for gases or flammable liquids shall not be used as an earth electrode. The metallic pipe of a water utility supply shall not be used as an earth electrode. Other metallic water supply pipework shall not be used as an earth electrode unless precautions are taken against its removal and it has been considered for such a use."

I'm thinking of a house I came across a while back that had an outhouse with water pipes in it, which were fed from the house (so privately owned I would assume). It also had an electrical supply provided by the house but without an earth supplied - instead, the earth was wired up to the metal water pipe in the outhouse. Does this regulation mean that the water pipe was perfectly viable as an earth electrode? I'd guess it's not considered great practice, but so long as it all tests okay it should be good to use?

The electrician I was with opted to put a separate earth rod in, which I guess would be the desired way to do it, but was it strictly necessary?
 
Last edited by a moderator:
the problem here would be if that water pipe was removed or replaced with plastic.
 
A family farm of mine is using the old bore hole piping as an earth rod.

1/2mile of buried pipe will be better than a normal earth rod.
 
the problem here would be if that water pipe was removed or replaced with plastic.

I read that as "yep, by the rule of the BYB it's permissible" (although possibly leaving yourself open to repercussions) but you also lead on to my next question:

"unless precautions are taken against its removal"

So what would be an appropriate precaution in the eyes of the BYB? A sign? Something documented in the (what will inevitably be lost by the tennant) electrical certs?
 
Last edited by a moderator:
since when would a wet-pants read an electrical cert? your mate did the right thing by banging in a rod. with a bit of luck it might give an acceptable RA.
 
Another reason, most people don't own the service pipes coming into their house, so they have no control over alterations.

It may well be a plastic joint added out on the road that reduces a perfectly good Ra to something not suitable.
 
since when would a wet-pants read an electrical cert? your mate did the right thing by banging in a rod. with a bit of luck it might give an acceptable RA.

I understand this Tel, and agree with his actions. Just trying to fathom the point of the regulation if most would say to stick a rod in instead - is this a regulation designed for a VERY specific use?
 
more a case of ensuring electrical safety if existing "unsatisfactory" means of earthing is removed.
 

Reply to Help with Regs in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top