Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.
 
Tell Your Mate He Is Talking Out His ---,of Course You Have To Have An Earth,they Work By Detecting Earth Leakage.
 
Tell Your Mate He Is Talking Out His ---,of Course You Have To Have An Earth,they Work By Detecting Earth Leakage.

correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke
 
why do you need a seperate earth to make rcd,s and rcbo's work?:confused: an rcd will actuate at around 22-30 milliamps, either of the phase conductors could come loose and touch exposed metal work which would allow the cpd to work,(connected to cpc or not),..... surely as scotty mentioned its a minute inbalance that would trip them....earth leakage that is. Non rcd/rcbo cpd's would require cpc for sure. Hope i'm not missing the point here:)
 
Last edited by a moderator:
everyone is a bit right - and some are a bit wrong here.

An RCD does not need an Earth per se, but needs an EARTH PATH

it is quite conceivable to have a house with no incoming earth, but there would be an alternaive path though the CPC to the MET, through the protective bonding and down to earth though any extraneous conductive paths (gas, water pipes etc)

as long as that path is 1667 ohms or less, the RCD would trip before the fault voltage reached the magical 50V, and even with a path of 7666 ohms or less would still trip.

Of course we need an earth path for CPD's to work correctly, but an RCD, with ANY path to earth as stated above, will trip off

and before anyone starts thumping the keyboard, I am NOT suggesting using an RCD means you dont have to have an incoming earth:p
 
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke
yes i know that but if there no earth path what then.:rolleyes:
 
Tr25 you say he has done his 17th, 17TH what ??Joint before Breakfast!! (and I'm not talking crimped)Anything without an earth return becomes a special location that is not allowed under normal circumstances, ie domestic installations
 
Listen mate im on your side lol.Hes a wee know it all ---- who has done a 17th course and is spouting out all this crap all the time.trouble is he is so sincere about it half the guys at work are starting to believe him.He is adamant the new regs say that if the board is protected by an rcd or if individual circuits all have rcbos then there is no need for an earth because the rcd/rcbo will operate on the imbalance of live and neutral.
 
Listen mate im on your side lol.Hes a wee know it all ---- who has done a 17th course and is spouting out all this crap all the time.trouble is he is so sincere about it half the guys at work are starting to believe him.He is adamant the new regs say that if the board is protected by an rcd or if individual circuits all have rcbos then there is no need for an earth because the rcd/rcbo will operate on the imbalance of live and neutral.

ok, I have explained how an RCD COULD work without an incoming earth with an extraneous path of 7666 ohms or less (but probably not in the required time), but that is an accidental by-product of there being no earth in the first place

How the hell does this guy think ADS will be achieved:eek:

I teach 17th edition, and this guy is talking utter tosh

he has no doubt misenterpreted something he was told on the course

along the lines of RCD protected circuits only needing a Zs of 1667 ohms or less for their 60898 MCB's etc etc

If you want to 'douse his flames' a little, ask him for the relevant regs numbers to back up his 'theories';):p
 
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke

I agree it will trip if the phase and neutral currents are not the same, however I would not sign off an installation without an adequate earth path unless it was SELV for instance You sure this guy isn't on about bonding? not done my 17th conversion yet but there was take about there not being a requirement for bonding in bathrooms anymore
 
Last edited by a moderator:
I agree it will trip if the phase and neutral currents are not the same, however I would not sign off an installation without an adequate earth path unless it was SELV for instance You sure this guy isn't on about bonding? not done my 17th conversion yet but there was take about there not being a requirement for bonding in bathrooms anymore

bit more complicated than that Moog, for bathrooms, but yeah, if all conditions are met, then no supplementary
 
O.K. it seems that there is some agreement on the workings of an RCD on this post.

An RCD protects by constantly monitoring the current flowing in the live and neutral wires supplying a circuit or an individual item of equipment.

The supply and the load are both connected to EARTH

Under normal circumstances, the current flowing in the two wires is equal. When an earth leakage occurs due to a fault in the circuit or an accident with the equipment, an imbalance occurs and this is detected by the RCD, which automatically cuts off the power before injury or damage can result.

If there is an imbalance in a circuit protected by the RCD, the leakage current has got to be going somewhere. If there is no earth path to take the current to earth, what is going to take it there? a person who recieves a shock from live metal work? :eek:

I think your friend should study the 16th Edition before trying the 17th Edition.
 
Like I said Warren, there may be an 'accidental' earth path through any extraneous paths, which, if 7666 ohms or less, would still allow the RCD to trip, but it is most defintely NOT in the 17th that you dont need an inscoming earth because of it:p
 
I think your mate is confusing a Main supply earth and equipotential bonding. The 17th does not require you to install equipotential bonding to pipes such as a bath room basin as long as the circuits in the bathroom are protected by an RCD. Every installation must have a main earth.

Sorry, meant supplimentary bonding not equipotential.
 
Last edited:
shakey, i understand about the 1667 ohms bit, but, shouldnt it be lower than that (exact figure not known at mo) to do away with an unreliable earth path??
 
shakey, i understand about the 1667 ohms bit, but, shouldnt it be lower than that (exact figure not known at mo) to do away with an unreliable earth path??

depends what you mean by 'do away with'

No value would allow you to do away with an unreliable earth

Or are you refering to the value of 200 ohms for TT earth electrodes?

This is the max value at which it could be condidered a 'stable reading', but is not a max value as far as the RCD is concerned

there is no 'leeway' for an unreliable earth
 
Technically an RCD will operate without any form of earth path being installed. It operates. as stated in other answers, by monitoring the phase and neutral and reacting to an imbalance between them. Normally this imbalance is as a result of an "earth fault" be it to a back box, cpc, or as a result of external influences like moisture. It is possible to have a created imbalance, for example where wall lights have been installed and the live is taken from the lighting circuit and the neutral is taken from a socket on the final ring circuit protected by an RCD (16th edition style split load board with protected and unprotected ways). By switching the wall lights on an imbalance is created on the final ring circuit which will trip the RCD. Whilst not a common fault it is a typical "lash up" job by a "Barry the Bodger".
 
Technically an RCD will operate without any form of earth path being installed. It operates. as stated in other answers, by monitoring the phase and neutral and reacting to an imbalance between them. Normally this imbalance is as a result of an "earth fault" be it to a back box, cpc, or as a result of external influences like moisture. It is possible to have a created imbalance, for example where wall lights have been installed and the live is taken from the lighting circuit and the neutral is taken from a socket on the final ring circuit protected by an RCD (16th edition style split load board with protected and unprotected ways). By switching the wall lights on an imbalance is created on the final ring circuit which will trip the RCD. Whilst not a common fault it is a typical "lash up" job by a "Barry the Bodger".

yup, done a few like that Tony

"just installed a new circuit, RCD trips as soon as i switch it on"

Investigation finds that the guy didnt know there was seperate neutral bars:eek:

Doh!
 
Not sure certain CU manufacturers are aware of this fact either! I've found several new CU's to have the neutrals connected arbitrarily to whatever bar suits at the time of manufacturer.
 
Modern (current controlled) RCDs make the assumption that any imbalance in line and neutral currents must be flowing to earth (because generally there isn't anywhere else for it to go) they don't actually measure anything with reference to the main or cct cpc's. However it still doesn't remove the fact an earth path must be present or there would be no residual current and the device would not operate.
I think the older voltage controlled ELCBs sensed voltage on the cpc but they were effectively proscribed in 1981 as it was realised that a parallel earth path would render them inoperable under true fault conditons.

Ask your man to draw out the FULL fault path and ask him were exactly does he thinks that inconvenient stray, 'residual' "I delta n" tripping current is going.
 
Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.


what about disconnection times?
 
As stated, there has to be an Earth path. That Earth path could theoretically become you.
 
The Only THEORETICAL reason that I can think of is that, if the fault trip coil on the RCD was to become faulty and the RCD did not trip then the touch voltage on a faulty piece of equipment may rise above 50V. Thus EEBADS would come into play.

:rolleyes:
 
Last edited by a moderator:
The Only THEORETICAL reason that I can think of is that, if the fault trip coil on the RCD was to become faulty and the RCD did not trip then the touch voltage on a faulty piece of equipment may rise above 50V. Thus EEBADS would come into play.

:rolleyes:

SteveF1 gather you have not done the 17th yet as there is No such thing as EEBADS any more its ADS
 
SteveF1 gather you have not done the 17th yet as there is No such thing as EEBADS any more its ADS

ian.settle1
Your assumption that I have not done the 17th Edition is incorrect. Yes you are correct that EEBADS has been replaced by ADoS as an acronym buit there will always be EEBADS. Although it is not refered to in the 17 Edition it does not mean "ther is no such thing any more" Equipotential bonding will always be required where protection against electric shock (indirect contact) is provided by Earthed Equipotential Bonding and Automatic Disconnection of Supply (EEBADS).It will also be used where disconnection times for circuits cannot be met, and where circuits with differing disconnection times come from a common distribution board.
I think you missed the point of the original post.
Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.

Regards
Steve F1:cool:
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Help!!!!!!!!!!!!!!!!!!!!!!!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
30

Thread Tags

Advert

Thread statistics

Created
ThrownRazor25,
Last reply from
SteveF1,
Replies
30
Views
5,769

Advert

Back
Top