Does anyone know the BS number and charateristics of the big square henley incoming fuse used by the supply company. its about 6 inch square with side entry for the supply cable system is TN-S.
There is no info on it and i take it the main fuse is inside its sealed so dont know the size.
any help appreciated
the seals normally drop off,so you can check if your that bothered about it
i know they do!!!!!!:wink5:
but its tight as hell to get new tails in si going to get supply company to connect so dont really want a dropped off seal.
just want info to make certificate out, new tails are connected to old ones at mo but there slightly undersized
On rare occasions I have put unknown for the service head details, only when I've got 25mm tails though. (or 16mm and have checked that maximum demand is ok.)
If the information is not written on the head and you cannot open the fuse carrier then there is no way to tell what is in there and you have to put unable to verify. You could stay on hold with the DNO until they tell you they do not know, but hardly worth it.
If the tails to and from the meter are 25mm, Then its a 100A fuse
If 16mm, then 80A/60A
Type of fuse most likely bs 1361
Reply to Henley incomer in the UK Electrical Forum area at ElectriciansForums.net
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
davesparks
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...