To those who whose s electricity supply is TNC-S, what are the requirements regarding the resistance of the homeowners earth rod (stake or mesh).?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Hi Guys, I would firstly like to introduce myself. Name is Edmond Noonan. Looking forward to hearing from you all. in the The Welcome Forum area at ElectriciansForums.net
Bit late but welcome to the forum.
[/QUOTE
Appreciate th
Hi Westward. Thank you for the welcome. Never too late. If you have any views on the question I raised I would be delighted to hear themBit late but welcome to the forum.
To those who whose s electricity supply is TNC-S, what are the requirements regarding the resistance of the homeowners earth rod (stake or mesh).?
Hi James. It applies to all countries who have a TNCS supply system. (U. K., Ireland, Sweden, Aus., N. Z. just to name a few).What country does this question relate too?
Thank you Pete. And as I mentioned to the others, I would be very happy to hear your views on the thread I posted.Welcome to the forum Edmond
[automerge]1593858247[/automerge]I’m guessing in other countries the homeowner has an earth rod at they combined with the Tncs supplied to add insurance against a lost neutral?....but I’m not actually that knowledgeable with this countries electrical system let alone others so it is a guess ?......oh and welcome in @Edmond Noonan ?
Hi Baddegg,I’m guessing in other countries the homeowner has an earth rod at they combined with the Tncs supplied to add insurance against a lost neutral?....but I’m not actually that knowledgeable with this countries electrical system let alone others so it is a guess ?......oh and welcome in @Edmond Noonan ?
It’s not something we commonly use herein the uk, the loss of the neutral is not something I’ve experienced personally in my limited experience but I’d imagine a few people on here have, I’d also imagine the parallel paths of gas and water bonds would be beneficial in that situation (assuming they are metallic) but as things progress and more gas pipes are plastic as water pipes are in the majority now days it could become a problem, hang about mate someone a lot cleverer than me will be along soon no doubt ?Hi James. It applies to all countries who have a TNCS supply system. (U. K., Ireland, Sweden, Aus., N. Z. just to name a few).
[automerge]1593857718[/automerge]
Thank you Pete. And as I mentioned to the others, I would be very happy to hear your views on the thread I posted.
[automerge]1593857802[/automerge]
[automerge]1593858247[/automerge]
Hi Baddegg,
Thank you. You actually hit the nail on the head with your comment about the earth rod intended to be a type of "insurance" against a "broken neutral". That is the whole issue. It would of course be insurance against a broken neutral PROVIDING the resistance of the rod is low enough. In reality an alternative low resistance return path would require several of the "standard earth rods".
Hi Baddegg,It’s not something we commonly use herein the uk, the loss of the neutral is not something I’ve experienced personally in my limited experience but I’d imagine a few people on here have, I’d also imagine the parallel paths of gas and water bonds would be beneficial in that situation (assuming they are metallic) but as things progress and more gas pipes are plastic as water pipes are in the majority now days it could become a problem, hang about mate someone a lot cleverer than me will be along soon no doubt ?
Hi Baddegg,
Frankly, I have never questioned the role an earth electrode plays until I did experience a broken neutral. Like you I assumed that "someone a lot clever than me" (believe me, there are lots) knew something that I did, nt. Broken neutrals in Ireland are more likely than they would be in the UK because of our overhead supplies. In the UK, they are most often underground and hence less vulnerable. You are correct about the effect that the loss of the metallic services are having on an effectve return path.So far the various DSO, s do not appear to have a plan to compensate for the loss of the earth path that these disappearing metallic services provided.
[automerge]1593865813[/automerge]
Hi Telectrix,Hi James. It applies to all countries who have a TNCS supply system. (U. K., Ireland, Sweden, Aus., N. Z. just to name a few).
there's no requirement in UK for earth rods/electrodes to be added on a TNC-S system. this might come in an amendment to 18th . kerrching, another £80 for IET.