Hi I’m looking for the maximum permissible resistance reading of earthing rods | on ElectriciansForums

Discuss Hi I’m looking for the maximum permissible resistance reading of earthing rods in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 12, 2020
Messages
3
Reaction score
0
Location
Yorkshire
Hi could anyone point me in the right direction for the maximum permissible resistance reading for earthing rods?
 
Hi could anyone point me in the right direction for the maximum permissible resistance reading for earthing rods?
Depends on the (RCD) Residual Current Device thst follows,as your unlikely to meet max ZS on mcbs alone, however the iet say above 200 ohms may not be stable, so less than 200 and as low as possible.
 
Hi could anyone point me in the right direction for the maximum permissible resistance reading for earthing rods?
It depends very much on what RCD you are using, or even If you are using one.
For example, if the RCD is 500mA then a max Ra of 100ohms is classed as acceptable. See table 41.5 BS7671.

If you intend to use the rod as the sole means of ADS then it probably needs to be sub 1ohm. I realise this sounds silly, but I'm just making the point that more information is required to give an accurate answer.
 

Reply to Hi I’m looking for the maximum permissible resistance reading of earthing rods in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
694
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
The issue I was having turned out to be a faulty transformer on the pole 30m away... after hassling the northern powergrid (and having then visit...
Replies
9
Views
953
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
687
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top