went to work with a dude yesterday and there was hi tuff cable for cctv been choped in half which had been buried about 100mm under ground.

i told him hi tuff shouldnt be buried underground, am i correct in saying this???? and reccomended he used swa.
 
no wasnt in ducting, for a 35 meter run. anyway i installed the swa and bonded the gland to the earth connection via lug at supply end is this correct. i just doubt myself , he kind of threw me in and left me to it,..

another one, when i went to cef they only had ip rated plastic connection boxes..
 
Last edited:
Then if there was no mechanical protection then reg 522.8.11 have a read of it it I=p/u for buried cable.

Yes as long as you were not using the SWA of the armour for the CPC then just earth the SWA at the origin for earth protection.

You could have used a wiska box, why are you worried about just using a plastic box??
 
cheers will have good read when the new book comes out as i never bought the red one, due to green one in pipeline...

as regards to the plastic box it had rubber seals where the cable entered wich wouldnt of kept the integrity of the ip 55 rating.. and thge swa gland wasnt that tight. but as tight and secure as i could get it with my gread ideas.lol
 

Reply to hi tuff cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top