Hi,

I was testing 2 shops today. One had 2 x single phase CU's & one had 1 single phase CU, all supplied from the basement which had the 3 phases down there.
On one board the reading i got were all fine, but the other 2 i had a reading of Ze: 4.61 and Pfc: 59A. This is very high which means a lot of my circuits will fail on the Ze, but are ok for R1+R2. Anyone got any suggestions, as to why it maybe be so high?
 
Did you test R1+R2 of the sub-main supplying this DB??

Just to be clear, an installation has only one Ze, at the origin. What you have measured is the Zs of the sub-main circuit, AKA Zdb.
 
As lenny has said if Ze is fine, and your Zs (Zdb) at each sub board is dodgy, then you need to give your submains a real good coat of looking at. How is the earth cable terminated? is it onto a rusty old nut and bolt? I have seen some nasty stuff but, you will be surprised at how little corrosion or very slightly loose connections can have a massive impact on your test results.

Cheers............Howard
 
I had one with a sub board.SWA to a 100amp isolator.using the armour as earth they had banjo'd the SWA to the isolator and stuck a bolt and nut in.Took the earth from the board on to a supplied bolt on side of Isolator for Earth.Never put a loop between so we got pants loop imp readings!
 
As Sirkit Breaker states, even the slightest corrosion will cause huge problems. You basically have no earth at those boards. If you are only doing a PIR, its technically not down to you to repair, but, it would have been a great time to issue a danger notice to the client or end user and strongly suggest that they allow you to investigate further.
 
Hi,

I was testing 2 shops today. One had 2 x single phase CU's & one had 1 single phase CU, all supplied from the basement which had the 3 phases down there.
On one board the reading i got were all fine, but the other 2 i had a reading of Ze: 4.61 and Pfc: 59A. This is very high which means a lot of my circuits will fail on the Ze, but are ok for R1+R2. Anyone got any suggestions, as to why it maybe be so high?

The poor earth seems likely but I don't suppose there was a UPS supplying this suspect consumer unit (maybe for tills etc.)?
 

Reply to Hi Ze & Pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K
Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top