Hi everybody,

Ok, here is the picture.

Main house is TN-S
Ze is 0.25 ohms

There is a 16mm swa fed from a 60a isolator, which in turn is fed from 25mm tails into henley blocks.
The swa is clipped outside the side of the house, buried in the garden and along approx 25 meters into a small studio / storage area.

There, there is an 8 way c/unit. 100a main switch, 2x RCD's. 1 RCD controls the storage sockets ( 4 ) and the studio florescent tube.

The other RCD controls the sudio room sockets ( 4 ) and the storage florescent.

My mate who just completed the install, calls me and tells me that he is getting 1.17ohms when doing a Zs on the sockets !!

I go and see. The cables and sockets are in plastic trunking, so no problem there. I check again the Zs on the install at the c/unit and get 0.35ohms. Ok fine.

I remembered once, an old school sparks, who on site where we worked, had a similar problem and he changed the RCD's and got a lower Zs reading.

I pulled out 2 legrand 30ma RCD's from the van, connected them up, and low and behold Zs is now 0.43ohms on sockets !!!

I did carry out an insulation resistance test and final ring tests prior to connecting new RCD's, which all were ok, as its a new install.

Any thoughts, can this really lower the Zs ??? Do RCD's play a part when checking Zs ??

Thanks and regards,
Sav
 
I have seen this loads of times. I occasionally help my mate out on rewires etc, and he insists in using cheep consumers units where if you add the R1 & R2 to Ze they are often 0.5 - 0.6 ohms lower than the Zs taken with the meter. This inaccuracy can only be down to the RCD. I use different consumers units from him and never see that level of difference.

Ian
 

Reply to Hi Zs solved by changing RCD ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top