Hi everybody,
Ok, here is the picture.
Main house is TN-S
Ze is 0.25 ohms
There is a 16mm swa fed from a 60a isolator, which in turn is fed from 25mm tails into henley blocks.
The swa is clipped outside the side of the house, buried in the garden and along approx 25 meters into a small studio / storage area.
There, there is an 8 way c/unit. 100a main switch, 2x RCD's. 1 RCD controls the storage sockets ( 4 ) and the studio florescent tube.
The other RCD controls the sudio room sockets ( 4 ) and the storage florescent.
My mate who just completed the install, calls me and tells me that he is getting 1.17ohms when doing a Zs on the sockets !!
I go and see. The cables and sockets are in plastic trunking, so no problem there. I check again the Zs on the install at the c/unit and get 0.35ohms. Ok fine.
I remembered once, an old school sparks, who on site where we worked, had a similar problem and he changed the RCD's and got a lower Zs reading.
I pulled out 2 legrand 30ma RCD's from the van, connected them up, and low and behold Zs is now 0.43ohms on sockets !!!
I did carry out an insulation resistance test and final ring tests prior to connecting new RCD's, which all were ok, as its a new install.
Any thoughts, can this really lower the Zs ??? Do RCD's play a part when checking Zs ??
Thanks and regards,
Sav
Ok, here is the picture.
Main house is TN-S
Ze is 0.25 ohms
There is a 16mm swa fed from a 60a isolator, which in turn is fed from 25mm tails into henley blocks.
The swa is clipped outside the side of the house, buried in the garden and along approx 25 meters into a small studio / storage area.
There, there is an 8 way c/unit. 100a main switch, 2x RCD's. 1 RCD controls the storage sockets ( 4 ) and the studio florescent tube.
The other RCD controls the sudio room sockets ( 4 ) and the storage florescent.
My mate who just completed the install, calls me and tells me that he is getting 1.17ohms when doing a Zs on the sockets !!
I go and see. The cables and sockets are in plastic trunking, so no problem there. I check again the Zs on the install at the c/unit and get 0.35ohms. Ok fine.
I remembered once, an old school sparks, who on site where we worked, had a similar problem and he changed the RCD's and got a lower Zs reading.
I pulled out 2 legrand 30ma RCD's from the van, connected them up, and low and behold Zs is now 0.43ohms on sockets !!!
I did carry out an insulation resistance test and final ring tests prior to connecting new RCD's, which all were ok, as its a new install.
Any thoughts, can this really lower the Zs ??? Do RCD's play a part when checking Zs ??