hi having conducted continuity test on ring main readings are L-L(R1-R1)=0.21 N-N(Rn-Rn)=695 E-E(CPC-CPC)=0.35. small ring main 8 sockets in total 1 spur not causing rcd to trip and when each socket is tested when live with sok 32 no faults any ideas why neutral reading so high?????.
 
halving the ring matey. guess the mid point in the ring, and connect L-N from one half of the ring together at the board. then test at the socket. If you get a high reading (you already know its not the live), then you know which half of the ring the problem is in. you then follow the same step again to halve that half of the ring, til you find problem. if no problem on this half of ring, then follow same steps but on other half of ring!:)
 
As above almost certainly just a bad connection in one of the sockets.....if any have been altered since the original install start there....but with just 8 points shouldnt be too hard to find.
 

Reply to high continuity reading on ring main neutral legs any ideas???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top