OK - discovered yesterday (when British Gas came to install my new boiler) that the earth is very poor, up near 100ohms.

So I then start thinking and remember that the water pipe is now plastic and the earth comes from the water pipe.

So, first of all can I confirm what type of earthing arrangement I have will be TT? There is ONLY live and neutral coming from the main incoming cable, there is no collar or connection to the armour or a core (TN-S) and there is no link anywhere from the neutral to provide an earth (TN-C) and as before it is therefore not TN-C-S

So I need to resolve this ASAP. What are my options and the network owner are not interested unless I pay in the region of ÂŁ2000.

Earth rod?

I would also like to add at this point that the incoming cable is the old fibre and metal wrapped stuff, could I put a collar round it and use it as my earth?

I have access to a megger so I can test the earth once I have done this to make sure it is working.
 
Hi, regarding the option of creating TN-S by using the armour, can you not test the ZE of this first? If you get a satisfactory reading (max 0.8 ohms), then you can use that. In theory that is. Im sure that you have to have the cable owners permission. Also if the cable is old, which it sounds like, then the armour is probably badly corroded.
 
Yes, I could just test the armour first and see what reading I get; I will get the megger tonight and see what it says.

I appreciate that the network owner are the only ones that are allowed to touch their cables but in the interests of safety and not having lots of spare cash sitting about to get them to do it I think it is probably a risk I am willing to take as at least it won't be fatal if it gives the house a good earth.

If it is no good I guess earth rod time and some 10mm will sort it.

I read a minute ago a BS which implied that in TT systems anything less than 200ohms is within spec, is that true? If so then should British gas still carry out the works as the readings are within spec? I said 200 but more accurately is was more like 189Ohms.

 
You must not connect a clamp to the incomming lead sheath cable to obtain your earth.

If no earth is present you will need to install an earth as per TT.

When installed as long as the reading is under 200ohms (better closer to 100) then that is acceptable.
 
Hi, regarding the option of creating TN-S by using the armour, can you not test the ZE of this first? If you get a satisfactory reading (max 0.8 ohms), then you can use that.

As Jason has said no no no don't do it...also make sure an RCD is protecting the installation.
 
hi all, so just out of interest...the supplier is not duty bound to supply an earth? have the properties either side got tns/pme.?.its like in the osg it states electricity company isolator but when you want one fitting for safe isolation to rewire or change the c/u then most of them charge for what clearly states is theirs....moan over:)
 
They dont need an isolator. They have the fuse.

However, they are fitting them generally on new supplies, but these are normally in the form of a 'self connect' meter.
 
You must not connect a clamp to the incomming lead sheath cable to obtain your earth.

If no earth is present you will need to install an earth as per TT.

When installed as long as the reading is under 200ohms (better closer to 100) then that is acceptable.

I'll blast in the biggest earth spike I can buy - any tips on locations for spikes, some people mention near stack joints (soil pipe collector).

Thanks
 
Out of interest, why can you not use the lead sheath, with permission of course? is it because you cannot garauntee the correct connection of the sheath to earth at the other end of the supply cable?
 
Out of interest, why can you not use the lead sheath, with permission of course? is it because you cannot garauntee the correct connection of the sheath to earth at the other end of the supply cable?

I'ts because the only clamp generally available is a standard bonding strap which would crush the soft lead sheath into the paper insulated cores within........you really wouldnt want to be in the same room :eek::eek::eek:
 
i am in college just working through earth impedence. Aside from a meter to tell you what the ZE is, is there a forumlar for working it out...thanks
 

Reply to High earth impedance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
719
Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top