I

IMH

Hi iam testing an istrallation on a TT system, the ELP readings at the board are 223 ohms, when i conduct an rcd test on a secondard distribution board the rcd 30mA fails to operate. The earthing system is in place,IE water gas are bonded and there are four earth rods installed any sujestions??
 
Hi, welcome to the forum. What is the Ra of your earth electrode(s) ... 223 Ohms? If so you need to go much deeper with the rods, either extend the existing ones (if possible) or sink new ones.
Stability of a single rod earth electrode often causes confusion. The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a R[SUB]A[/SUB]=300 Ohms will be more stable than a 1.5m rod with a R[SUB]A[/SUB]=100 Ohms. Although BS7671 says <200 Ohms for stability this is not a guarantee, depth is the key as stated above, you should aim to get your Ra below 100 Ohms and the lower the better.
 
Last edited by a moderator:
If the RCD fails to trip you need to look at other causes...a 30ma RCD will operate at much higher earth loop impedances than 223 ohms,in fact it will meet the requirements up to 1667 ohms. Of course you need to improve the present Ra, but this will not be the cause of the RCD not operating.
 
Hi thanks for the advice:icon4:

Hi, welcome to the forum. What is the Ra of your earth electrode(s) ... 223 Ohms? If so you need to go much deeper with the rods, either extend the existing ones (if possible) or sink new ones.
Stability of a single rod earth electrode often causes confusion. The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a R[SUB]A[/SUB]=300 Ohms will be more stable than a 1.5m rod with a R[SUB]A[/SUB]=100 Ohms. Although BS7671 says <200 Ohms for stability this is not a guarantee, depth is the key as stated above, you should aim to get your Ra below 100 Ohms and the lower the better.
 

Reply to High ELP reading in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top