Hi iam testing an istrallation on a TT system, the ELP readings at the board are 223 ohms, when i conduct an rcd test on a secondard distribution board the rcd 30mA fails to operate. The earthing system is in place,IE water gas are bonded and there are four earth rods installed any sujestions??
 
Hi, welcome to the forum. What is the Ra of your earth electrode(s) ... 223 Ohms? If so you need to go much deeper with the rods, either extend the existing ones (if possible) or sink new ones.
Stability of a single rod earth electrode often causes confusion. The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a R[SUB]A[/SUB]=300 Ohms will be more stable than a 1.5m rod with a R[SUB]A[/SUB]=100 Ohms. Although BS7671 says <200 Ohms for stability this is not a guarantee, depth is the key as stated above, you should aim to get your Ra below 100 Ohms and the lower the better.
 
Last edited by a moderator:
If the RCD fails to trip you need to look at other causes...a 30ma RCD will operate at much higher earth loop impedances than 223 ohms,in fact it will meet the requirements up to 1667 ohms. Of course you need to improve the present Ra, but this will not be the cause of the RCD not operating.
 
Hi thanks for the advice:icon4:

Hi, welcome to the forum. What is the Ra of your earth electrode(s) ... 223 Ohms? If so you need to go much deeper with the rods, either extend the existing ones (if possible) or sink new ones.
Stability of a single rod earth electrode often causes confusion. The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a R[SUB]A[/SUB]=300 Ohms will be more stable than a 1.5m rod with a R[SUB]A[/SUB]=100 Ohms. Although BS7671 says <200 Ohms for stability this is not a guarantee, depth is the key as stated above, you should aim to get your Ra below 100 Ohms and the lower the better.
 

Reply to the thread, titled "High ELP reading" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High ELP reading
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
IMH,
Last reply from
IMH,
Replies
3
Views
1,094

Advert

Back
Top