Hi, welcome to the forum. What is the Ra of your earth electrode(s) ... 223 Ohms? If so you need to go much deeper with the rods, either extend the existing ones (if possible) or sink new ones.
Stability of a single rod earth electrode often causes confusion. The depth of a vertical rod is the decisive factor for stability as the effects of drying and freezing effect the upper part of the rod most significantly. Therefore a 3m rod with a R[SUB]A[/SUB]=300 Ohms will be more stable than a 1.5m rod with a R[SUB]A[/SUB]=100 Ohms. Although BS7671 says <200 Ohms for stability this is not a guarantee, depth is the key as stated above, you should aim to get your Ra below 100 Ohms and the lower the better.