Hi Firewalshy,
“High Integrity Earthing” is slang often used by sparks incorrectly in place of High Integrity Circuit Protective Conductors.
“Clean Earth” is a misnomer used by the IT crowd and by some electronic engineers (who should know better) meaning “noise free earth”, when what they actually have is anything but a noise free earth. If you want an explanation of this PM me mate as it's likely to be lengthy.
Hi Firewalshy,
"Clean Earth" is a misnomer used by the IT crowd and by some electronic engineers (who should know better) meaning "noise free earth", when what they actually have is anything but a noise free earth.
In their cosy world, there are usually two earthing systems. The "dirty earth" has all the general appliances and non-critical equipment connected to it. The "clean earth" has all the critical data systems grounded on it in the hope that no electrical noise will be found on this earth.
Most IT, computer and audio/visual equipment widely use switched mode power supplies and/or EMC filters. If you count how many SMPS units or EMC filters are connected to each earthing system, you will usually find >10 times the number of capacitors between the live conductors and "clean earth" as opposed to that found on the "dirty earth", each capacitor feeds leakage current and electrical noise into the earth system. Most of these leakage currents and electrical noise extend from the 50Hz fundamental frequency of the supply to up and beyond 250 kHz, because most of the leakage and noise is derived from capacitors that preferentially conduct as the frequency increases.
As the frequency increases so does the conductor "skin-effect", where the current flow is increasingly concentrated near the surface of the conductor, thus reducing the amount of conductor doing any real work. Because less conductor cross sectional area is doing real work, the apparent resistance of the conductor increases proportional to the ratio of used CSA/Total CSA. This means that round cables are about the worst possible shape to conduct high frequency noise current, the reason for this is the poor ratio of surface area/CSA. Perhaps now you appreciate why the best lightening down conductors are made from flat copper bar, in order to conduct the extremely fast rise time current pulses.
Oh, the observant are probably thinking to themselves "my earth cable is multi-core, so every strand behaves like this, so my total surface area is multiplied by the number of strands?" Unfortunately you would be deluding yourself because the "skin-effect" acts on the overall diameter of closely spaced conductors in a multi-core cable as if the conductor was solid. At only the 5th harmonic, 250Hz, strongly associated with SMPS units, even round conductors of 25mm[SUP]2[/SUP] start to be degraded by the "skin effect".
Therefore, in summary, unless the "clean earth" system is constructed of substantial flat copper bar, similar to that of lightening conductors you are just wasting your time, because it will not be noise-free and the high frequency noise current will not be conducted to earth.