Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
That would be 4mm wouldn't it?
 
I would more than likely add them together and make a note on the cert reflecting the amount of cables on the circuit.
 
That would be 4mm wouldn't it?
I think Pete is correct there being a minimum of 4mm single earth when protected against mechanical damage.
If you are saying you have a 2.5/1.5 radial with a 2.5mm earth from the end of the radial to the distribution board I would put down 1.5 as the circuit CPC. What is the installation method?
 
Only time I've done this has been using the two separate CPCs of a RFC using different terminals inside the D.B as per 543.7.1.204

I've been asked to test a load of high integrity radial circuits with two separate (different sized) CPCs.

My question is, in the box which asks for the CSA of the CPC, do you just write that of the radial and make a note of the other size in the comments or do you add the two CSAs together.

My initial thought was add them together but then I thought we dont write 3mm when installing a 2.5/1.5 RFC.

Any advice welcomed
Because that’s just one conductor.
 
That would be 4mm wouldn't it?
I think he is referring to the 1.5/1.5 of a ring final circuit. It depends on the schedule format you are using and whether you can insert all conductor csa. I like to include all as I hand write them so if you have a 2.5 T&E with a separate 4mm cpc I would put 1.5/4.0
 

Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

Similar threads

Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
432
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top