Hi

ive been at my mates today between Boston and skeggy in the middle of knowhere surrounded by cabbages.

hes on the very end of an overhead supply, it's PME.

the Ze is 0.56 ohms, would you say this is a big on the high side? I know it's on a long run and they can be high but just wondered what your thoughts were.

ivd just been putting a sub main up to some out buildings and a caravan pitch and earth rods, quite pleased as put one heap of 4 x 5/8 rods and got 5.7 ohms!
 
Pull the fuse and see what size it is. You may be able to go down a size load dependent of course.

If not I presume you would have to treat it like a TT?
 
the earth rod was at the remote end around 80 meters from the cut out where the caravan pitch was, thats the only TT bit on the installation.

I had just ran a 16mm submain from a 63A switch fuse at the cutout to the out building up the field thats all, but thats on the supply earth.

It was just the measured Ze at the switch fuse at the supply end that I felt was out of parameter, like I say i know they can be a bit higher than specified top end figures, but wasn't sure how much over you would say is acceptable.
 
My youngest is a Western Power technician. For a pme connection their policy is - below 0.35 connect, between 0.35 and 0.8 to connect and advise.
Don't think you will get much joy from the dno
 
Hi,

What has the fuse size got to do with it?

TNS = 0.8
TNCS = 0.35
TT = 200~

Its out of parameter for the supply type? Or am i being thick and missing something?

It is a PME supply, its got an 1362 Type II b 80A fuse.

Those are BS7671 values, not the DNO's.

They will most likely have their own.

You understand why you need low impedance for a given OCPD so the same must apply for the fuse in question shouldn't it?

Every DNO have their own rules.
 
Last edited:
The fuse must be in a very big plug top.

Have you not seen the PME plugs?

[ElectriciansForums.net] High ish Ze
 
Hi,

What has the fuse size got to do with it?

TNS = 0.8
TNCS = 0.35
TT = 200~

Its out of parameter for the supply type? Or am i being thick and missing something?

It is a PME supply, its got an 1362 Type II b 80A fuse.

The Ze guidelines are different for different fuse sizes, it's a bit scary that you need to ask that, do you not understand the point of earth fault loop impedance?

I think from memory the guideline for an 80A supply is in the region of 0.5/0.6, but the DNO will confirm as it is dependant on their own internal guidelines.
 

Reply to High ish Ze in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top