Looking for a bit of advice going at the back of a company who carried out a periodic in a shopping centre.
In the observations they have listed as a code 1 that the Ka rating of the MCBs are unsuitable for all the circuits in the DB as they are 3Ka with the PSC 4.8Ka.
But i thought the 4.8Ka would be in reference to the supply MCCB feeding the DB rather than the individual MCBs contained within the DB.
To establish if the 3Ka mcbs were inadequate it would be the end of each cicuit fed from each MCB.
Am i enterprating that right?Cheers for any help.