Hi Guys
Any advice would be much appreciated!

I have tested a property that has a PFC greater than the short circuit capacity of the mcb's protecting the final circuits, the PFC is 7.9KA and the 60898 mcb's 6KA. The property is protected at origin with a 1361 type b fuse 16.5KA. Under the regs as i understand them the protective device must have a short circuit capacity greater or at least equal to the PFC, therefore am i wrong in assuming that i advise the client that the mcb's protecting the final circuits are upgraded to 10KA or not?:confused:
Would the 1361 fuse with a higher breaking capacity and similar fusing factor to the mcb protect the installation or not, also would this mean a lot of domestic properties that are situated close to substations but with "run of the mill" 6KA mcb's require upgrading??​
 
The 1361 fuse at the origin will offer sufficient protection against fault current. There is no need to change the MCB's.
 
Another point worth considering is that your pfc has a linear relationship with your Ze and that will almost always be at the origin of the supply ie at the incomer.
In practice a fault within the instalation itself would never generate such high currents because of factors such as cable resistence ect.
It is highly likely that the mcb would disconnect the supply way before its 6k limit. And as Sintra said, the let through current would be governed by the primary device 1361 fuse at the cutout.
 
Hi. I know this an old post but have just come across the same problem and the highest reading is 19.9kV. So to comply the breakers MUST be higher than the potential fault current otherwise the breakers will be damaged if they disconnect because of this. Or so I think! Anyone know where the regs say different please?
 

Reply to High PFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
796
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top