The reason I ask is that even though the MCB's are only 6KA if they are in a consumer unit To BS 60439 and protected by a BS 1361 type 2 suppliers fuse then the whole assembly is tested upto 16KA.
Here is a snippet of annex ZA......
In the UK, such equipment is referred to as a ‘Consumer Unit’
and as such is covered by this Standard. However, additional
requirements from annex ZA of the standard call for the
assembly to have an additional test; this is known as the
‘conditional withstand test’. The condition is that the consumer
unit must withstand a 16kA short circuit fault when protected by
a 100A HRC fuse to BS 1361 type II. Further requirements are
addressed by this annex:
• Means of isolation to be via a manual double pole switch
disconnector
• Rated current of consumer unit is determined by current
rating of incoming device.
• Outgoing protective devices can be MCB’s, Fuses and/or
RCBO’s.
* No diversity factors are applicable to consumer units, the
incoming circuit and the bus-bar system must be able to carry
their full rated current without exceeding the temperature rise
limits.