Hi all
i have a question regarding a high pfc and installed mcbs. can i rather than replacing every mcb incorparate a main breaker equal to the pfc ?
 
i think its called cascading. yes you can, and its often done in industrial jobs, and on certain domestic jobs where the DNO fuse is used.
the problem is ensuring that all of the electrical gear upto that point can take the fault current without bursting into flames, or causing serious damage.
 
yes the pfc is 11ka on l-n and 5 ka l -e the current devices are rated at 6 ka so rather than replace all mcbs i wanted to incorparate main breaker at 15 ka does this sound acceptable ?
 
The reason I ask is that even though the MCB's are only 6KA if they are in a consumer unit To BS 60439 and protected by a BS 1361 type 2 suppliers fuse then the whole assembly is tested upto 16KA.

Here is a snippet of annex ZA......

In the UK, such equipment is referred to as a ‘Consumer Unit’
and as such is covered by this Standard. However, additional
requirements from annex ZA of the standard call for the
assembly to have an additional test; this is known as the
‘conditional withstand test’. The condition is that the consumer
unit must withstand a 16kA short circuit fault when protected by
a 100A HRC fuse to BS 1361 type II. Further requirements are
addressed by this annex:
Means of isolation to be via a manual double pole switch
disconnector
Rated current of consumer unit is determined by current
rating of incoming device.
Outgoing protective devices can be MCB’s, Fuses and/or
RCBO’s.
* No diversity factors are applicable to consumer units, the
incoming circuit and the bus-bar system must be able to carry
their full rated current without exceeding the temperature rise
limits.
 

Reply to High PFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top