S

sparkinlee

A fuse box I was working on the other day (doing such things as providing a main earth connection to the fuse box, which I can only assume was missing for years) looks like this:
[ElectriciansForums.net] High PFC

Having installed the main earth, the PSSC is 8.5kA. Must be close to the transformer...

The mcb 3rd from the left in the picture is shown to have a rated short circuit capacity of 3kA, and I assume the others are the same, and accordingly all are lower than the PSSC.

As far as I can see the simplest remedy would be to replace the push in MCBs with push in fuse carriers and BS 1361 fuses with a rated capacity of 16.5kA according to the onsite guide. Any other suggestions?

If the client requests information on upgrading to a 17th Edition board, who makes MCBs that would be suitable? - my recollection at this time of night is that they are generally 6kA, which would be too low.
 
Hager make a full range of 10kA mcb's, and even (I think) 15kA.
 
bear in mind that the MCBs have to withstand the fault current on their respective circuits. the 8.5kA would only occur downstream of the MCBs if the fault was very close to said MCBs. generally we calculate/measure the fault current applicable to the MCBs from the furthest point on each circuit.
 
i=p/u, read my post. it is upstream of the MCBs that you get the 8.5kA, yes, but also downstream, close to the MCB, the pfc would be close to that figure. at the extremity of the circuit, it would be considerably lower due to the circuit impedance.
 
I've always thought that it kind of doesn't matter - the 6/10/15/whatever rating is the maximum fault current that the device will switch AND STILL OPERATE afterwards, though we all know that it'll in all likelihood be toast. So, if you're going to fry it, it's fried and therefore doesn't matter.
 
I think the conditional rating is more to do with safe operating limits, in reality the fault rating of a device is usually not a worry as its never going to reach the 33kA of the service fuse.
 
I thought that if the main fuse was a BS1361 type II that this would have a Maximum capacity of 33Ka and would subsequently allow individual mcbs 16Ka downstream?

Sent from my GT-I9100 using Tapatalk
 
The 16kA rating of CUs applies to type tested CUs, which are tested with CPDs installed.
I don't know whether these old domino style CUs were ever type tested, or whether the CUs have been type tested with the plug in MCBs installed.
It's something you would have to confirm with the manufacturer.
Here's a link to a publication that gives some information: http://uk.search.yahoo.com/r/_ylt=A0geu8UC98ZOtXsAw2FLBQx.;_ylu=X3oDMTBzdTNjcXU5BHNlYwNzcgRwb3MDMTAEY29sbwNhYzIEdnRpZAM-/SIG=132o8aia5/EXP=1321691010/**http%3a//www.beama.org.uk/download.cfm/docid/1861A011-BADD-4874-9B0F246FC31F490F
 
Good News:
The Wylex MCBs are all BS EN 60898 Type B and the Wylex distribution board is BS5486 Pt13, 8way. According to the latest Wylex Catalogue the BS5486 Pt13 designed board is considered a factory built assembly to BS EN 60439-3 when fully assembled, and therefore the above combination has been fully type tested to that specification.
 
Last edited by a moderator:

Reply to High PFC in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top