I’ve just been to look at a job where the client wants to have a couple of extra sockets fitted.
The consumer unit is an old rewirable with no rcd protection, but there is a new garage rcd/mcb board fitted next to it with a spare way that was installed just 2 weeks ago by their landlords electrician when he installed an electric heater.
Ok, should be easy, just test the existing circuit that I’m going to extend and put it into the new board on a 32 amp mcb.
The electrician only installed 16mm tails and 10mm earth but I can easily up grade these, the problem I have is that I did a quick Ze and got a very low reading of 0.04 ohms. This prompted me to do PFC test and I got a result of 11Ka.
Now, the new garage has domestic 6K breakers fitted, I know I can get 10K mcbs but I do not know of anything with a greater breaking capacity.
Any ideas ?