Hi all advice is greatly welcome
I originally had reading of PSCC 19kA until I returned my meter to Megger who have sent it back repaired and recalibrated.
I have a high PSCC 7.2kA this is on a TN-S system there is a sub station about 340 metres away CU is a wylex dual RCD jobby the breakers have a breaking capacity of 6kA.
Mains fuse is a BS 1361 Type II
The PEFC is below 4kA
and Ze =0.05 ohms
The actually question is what shouid I do
Do I need to replace all CU components to accomadate this current ie above 6kA breaking capacity.
I appreciate any advice all knowledge is an improvement