Did some testing and my readings on 3 phase psc was like 6.7Ka, is that normal? as I find it rather high? thats between 2 of the phases, whats the reasons for this? and is it the suppliers fault for it being so high, What is an average PSC reading on a three phase and single phase anyway?
 
your reading can be high especially if your close to sub station
if it goes over max permissable for device(mccb) try bs88's as they have a higher Ka rating
 
Luke

NO NO NO NO

repeat after me

NEVER TEST PSCC BETWEEN PHASES

most test meters operate on 230V. You have just banged 400V accross it. Not good.

Measure PSCC Line to Neutral as you would with single phase, then double it to get your three phase value.

Dont forget your PFC's are just mathematical evaluations of Ze or Z.

I = V/R

where I is PFC and R is Z or Ze

so for a Ze of 0.5 ohms for example I would be PEFC would be 460A

If you were to measure Z (between line and neutral) and use this value, it would give you PSCC, which would then be doubled for a threr phase system

Most 60898's i have seen are rated at 10KA so you are fine
 
some meters DO test phase to phase (metrel if memory serves)
and your right dont test at 230 across 400 bang new meter please!!
 
Luke

NO NO NO NO

repeat after me

NEVER TEST PSCC BETWEEN PHASES

most test meters operate on 230V. You have just banged 400V accross it. Not good.

Measure PSCC Line to Neutral as you would with single phase, then double it to get your three phase value.

Dont forget your PFC's are just mathematical evaluations of Ze or Z.

I = V/R

where I is PFC and R is Z or Ze

so for a Ze of 0.5 ohms for example I would be PEFC would be 460A

If you were to measure Z (between line and neutral) and use this value, it would give you PSCC, which would then be doubled for a threr phase system

Most 60898's i have seen are rated at 10KA so you are fine

Most of AVO(MEGGER) you can test between phases go up to 440volts
 
Most of AVO(MEGGER) you can test between phases go up to 440volts

Yes I agree Ian, some meters will, and some meters wont. And some people dont know the difference. So adopting the standard practice (as per GN3) of measuring phase to neutral and doubling the value to obtain equivalaent three phase value is a good deal in my book.

It GUARANTEES the meter aint gonna go pop!:eek:
 
pscc is done either with 3 leads or 2
if you are using 3 leads the black and green lead goes in the neutral and the red lead in the phases
take all 3 readings and then double the highest
if you look in guidance note 3 it say that in a 3 phase system the pscc will always be the higher than pefc because as a rule of thumb you double it
 
Yes I agree Ian, some meters will, and some meters wont. And some people dont know the difference. So adopting the standard practice (as per GN3) of measuring phase to neutral and doubling the value to obtain equivalaent three phase value is a good deal in my book.

It GUARANTEES the meter aint gonna go pop!:eek:

3-phase psc measurements aren't really that difficult. It strikes me that if you are live testing you should know how to use your instruments and know its limitations. (see GN3 for advice).

The old Robin loop testers will give you a firework display, without warning, if used to test 3-phase psc, but the newer Flukes, Meggers, and Metrels are usually Ok.
 

Reply to high PSC? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

https://sravivarman.com/technical-articles/parallel-operation-of-thyristors/ Series resistor, or bigger series resistor, needed?
Replies
1
Views
153
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top