Hi All,
Can any body advise why i am getting a reading for PSCC L-N of 10KA ??
 
Assuming that you have a voltage of around 245V, that's roughly a Ze of .025 - unusual but not impossible. Whereabouts are you / site?
 
What instrument are you using?
I ask because I had a Fluke 1652 on long term loan which was fine on L-E PEFC but nearly always gave ">10kA", ie off the scale, for L-N PSCC. My current Fluke 1652C seems to be behaving itself.

Edit:
This was usually on a TN-C-S supply where the two values should be near enough the same.
 
Last edited:
West yorks, semi on private estate on edge of moors, no sub station near by that i'm aware of.

If you don't know the length of the supply cabling then you can't calculate the PSCC manually so you don't have much choice but to trust your test results. The reading of 10KA doesn't strike me as extraordinary so I wouldn't lose any sleep over it. A private estate will most likely have its own substation in close proximity.

*Edit* Wouldn't a high PSCC on the supply be a DNO problem anyway and not yours?
 
Last edited:
If the supplied distribution board and protection devices are suitable for that level of PSCC then there is no problem. Remembering that the Short circuit capacity of OPD <50A in a CU to BS60439-3 or BS5486-13 with a BS1361 type 2 suppliers fuse can be considered to be 16kA.
 

Reply to High pscc ???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top