High R1+R2 | on ElectriciansForums

Discuss High R1+R2 in the Australia area at ElectriciansForums.net

lurch

-
Joined
Feb 5, 2009
Messages
276
Reaction score
39
I have a customer who recently had a test an an inspect on his new house. the report showed a high r1+r2 reading on the shed suply. I have checked it out and cant find anything obvious that would suggest why the reading is high on the cpc. however I cant get to a JB that is concealed behind a newly installed kitchen which seems to be the only obvious place the fault can be (the JB apparently is an adaptable box chnaging the t&e to swa, which I reckon is probaly a loose gland on the swa/adaptable box). My suggestion is to provide a earth rod at the shed. the circuit is RCD protected. . . . . thoughts please.

Lurch
 
how high is r1r2 because the armour on the swa should be earthed could the loose connection eventually fail leaving it un earthed

i wonder if you could earth the armour back of the new stake?
not sure this is ok though

I havent got the test sheet avaialbel but recall it being around 300ohms. the armour will pick up the earth at the adaptable box from the t&e assuming thi shas been done properly. Yes, if I put a stake in I will earth the armour. ps the supply to the property is tns.
 
Doubt you will get away with that part of the property would be tns the other tt giving you an unequal potential at the property.

Junction box should be accessible at all times and if you work on the circuit you take responsibility for it

Hope that helps

Chris
 
Doubt you will get away with that part of the property would be tns the other tt giving you an unequal potential at the property.
Chris, could you confirm why this would not be acceptable.

Junction box should be accessible at all times and if you work on the circuit you take responsibility for it

Hope that helps

Chris

And agreed the JB should be accessible at all times. Unfortunately I did not carry out the original instal of the shed feed or the kitchen install. I am trying best to sort an issue with least disruption possible.

Thx again
 
Never heard of it being acceptable and I cant find anything in 17th edition that would allow it you either has a tncs, tns or tt not a mixture.

As for the junction box if you touch that circuit you assume responsibility for the entire circuit best to ring the NICEIC or whoever you are registered with to see if noting that on your certificate would suffice.

Chris
 
Chris,

This is often done if there are metal services in a garage for example, and saves running a separate 10mm earth bonding cable back to the house MET.

Of course, this is all if the supply cable to the shed/garage is not adequate.
 
Just wondering Lurch did you check that the cpc was completely responsible for the high R1+R2 and can you or anyone explain how you now test R1+R2 with a TT system or do you not have to?
 
can you or anyone explain how you now test R1+R2 with a TT system or do you not have to?

:confused: same as you would any other system, link line and cpc of required circuit at DB and measure at furthest point on circuit if radial, if ring link P1 and E2, P2 and E1 and measure at each socket outlet recording the highest as R1+R2.
 
Last edited by a moderator:
:confused: same as you would any other system, link line and cpc of required circuit at DB and measure at furthest point on circuit if radial, if ring link P1 and E2, P2 and E1 and measure at each socket outlet recording the highest as R1+R2.

Probably just me being dim, but was thinking about the previous scenario in the shed that is now earthing through an earth spike - would there have to now be a new small CU in the shed ? If not the Phase and cpc are going to be nowhere near each other to link :eek:
 

Reply to High R1+R2 in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top