Crikey, you think it's just a quick one?
There are two main reasons for providing RCD protection.
One is to provide additional protection for circuits of special locations, socket-outlets and cables concealed in walls.
This applies irrespective of whether the installation is TT, TN-S or TN-C-S.
BS7671 requires that such a device be rated at 30mA and operate within 40ms when the operating current is 150mA or greater.
Another reason for using RCDs, is where the disconnection times as specified in BS7671 cannot be achieved by use of an Overcurrent Protective Device, due to high Zs.
Typically in TT installations where distribution circuits require 1s and final circuits require 0.2s (200ms).
RCDs are very sensitive, and many appliances have earth leakage in normal operation.
To prevent the cumulative earth leakage of a number of appliances from causing nuisance tripping, we are required to divide installations into a number of circuits.
However this still leaves distribution circuits requiring the use of RCDs to achieve disconnection times being subjected to the earth leakage of a number of appliances.
To prevent nuisance tripping on these circuits, a higher rating is used, typically 100mA.
However, by doing such, we would have RCDs in series, which will cause discrimination problems in the event of an earth fault. Something that BS767 also requires us to address by dividing installations into separate circuits.
Generally earth faults are of such a high amperage, that they would cause any RCD to operate whatever the rating.
To provide discrimination, for earth faults, time delayed RCDs are used.
As such this would entail a 100mA time delayed RCD protecting distribution circuits, with 30mA RCDs protecting final circuits and socket-outlets.
If the distribution circuit also required additional protection due to being concealled in a wall, another method of additional protection would have to be provided.
To test time delayed RCDs using most MFTs, you have to set the device for RCD test, then toggle through the options for type, rating and time for the particular RCD being tested.