Hi, I was wondering if you guys can help with some errant test results.

I'm testing a ring and i get
L-L = 0.41
N-N = 0.40
E-E = 0.63

Great

Figure 8 L-E = 1.0 ohms.

Still good

Figure 8 at each socket varies from 0.8 ohms to 1.1 ohms (I was expecting much lower)>

Oddly Zs = 0.23 (which is what I was expecting for both this and my R1-R2 [at socket] tests.

Any ideas?? System is TNS / Ze of 0.09

Maudy
 
your fig.8 R1+R2 should approximate (r1+r2)/4 so your 1.0 ohms looks high. are you sure you have nulled leads for the R1+R2 readings?
 
make sure you null leads are you on right legs of ring your fig 8 should be aprox 0.26 given the values you have given the reason the readings might be different at various points is possible spurs
 
check at terminals of outlets as i installed a load of mk sockets and readings at fron varied wildly
N terminals were hard work to screw down plastic seemed to be restricting it

ended up removing them all and replacing with BG

also as you say your reading increased was this to the mid point of the ring as you could have incorrectly identified the legs and not carried out cross connection correctly
your R1 +RN should be more like 0.2 and your R1 +R2 should be around 0.26ohms or within 0.05 ohms of each other so 1.0ohms to high
 
How are you measuring your figure of eight? It sounds asthough you are disconnecting the cables from the sockets and measuring 2 end to ends as the results are your L-l and E-E added together
 
How are you measuring your figure of eight? It sounds asthough you are disconnecting the cables from the sockets and measuring 2 end to ends as the results are your L-l and E-E added together

Mhahaha

Yea - its wired in T&E so I wouldn't make that mistake.

It not that the socket readings start off low and get higher - they're all too high. Or as I suspect the figure 8 end to end (measured at the board) is too low. WHich makes me think Murdoch is right.
 

Reply to High ring test results at socket outlets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top