I
IronLiver
Has anyone had any experience with increased voltage levels caused by PV systems affecting any of the installed equipment on site? Had to reset an SB 4000TL to G83/1 on a domestic install recently as the voltage levels were to high for the G59 settings particularly on sunny days. There seem to be a few PV installs in the area, which may be pushing up the voltage at the transfomer?
Voltage at the AC isolator for the PV system (with inverter switched off) was 244V at last measurement, which is within the +10% tolerance that the DNO is allowed. When the PV system is on the voltage rises to around 249V, but must have gone higher on occasions as the inverter was cutting out under G59 stating an error code of 103 - Grid overvoltage slow. Anyway after a lenghty exchange with SMA got the necessary code and reset to G83.
During the visit the customer told me that he has had 5 Honeywell motorised zone valves die in the last month (all now manually opened). I took a look and these motors are rated at 230-240V, could they have been damaged by the high voltage levels in the installation? Has anyone experienced this before? I stopped short of measuring the voltage at the motor/boiler spur.
Customer is not keen to replace the motors if there is a chance they will be damaged by high voltage levels. That said I have frequently recorded voltage levels in excess of 240V at CU despite being 230V nominal.
Any advice gratefully received.
Cheers
Monty
Voltage at the AC isolator for the PV system (with inverter switched off) was 244V at last measurement, which is within the +10% tolerance that the DNO is allowed. When the PV system is on the voltage rises to around 249V, but must have gone higher on occasions as the inverter was cutting out under G59 stating an error code of 103 - Grid overvoltage slow. Anyway after a lenghty exchange with SMA got the necessary code and reset to G83.
During the visit the customer told me that he has had 5 Honeywell motorised zone valves die in the last month (all now manually opened). I took a look and these motors are rated at 230-240V, could they have been damaged by the high voltage levels in the installation? Has anyone experienced this before? I stopped short of measuring the voltage at the motor/boiler spur.
Customer is not keen to replace the motors if there is a chance they will be damaged by high voltage levels. That said I have frequently recorded voltage levels in excess of 240V at CU despite being 230V nominal.
Any advice gratefully received.
Cheers
Monty