Hi all
changed a consumer unit today all circuits protected by rcbos.
Done all the usual tests, all good until i came to my Ze and Zs, its a TNC-S system.when testing ze my readings varied from 0.49 to 0.72.Iam NOT OUT IN THE MIDDLE OF THE WOODS!!I then procedeed to the Zs to see if i was getting a reasonable reading compared to my r1,r2, but when i tried to test zs the rcbo for the circuit under test kept tripping,sockets ,lights,heating e.t.c???? i have checked all the rcbos, no earth leakage and all trip within time!! my ? is, is there a problem on the supply side where the earth is maybe breaking down?? or is my brand new all signing and dancing meggar goosed???.
And this is not flats either!!!
Thanks
changed a consumer unit today all circuits protected by rcbos.
Done all the usual tests, all good until i came to my Ze and Zs, its a TNC-S system.when testing ze my readings varied from 0.49 to 0.72.Iam NOT OUT IN THE MIDDLE OF THE WOODS!!I then procedeed to the Zs to see if i was getting a reasonable reading compared to my r1,r2, but when i tried to test zs the rcbo for the circuit under test kept tripping,sockets ,lights,heating e.t.c???? i have checked all the rcbos, no earth leakage and all trip within time!! my ? is, is there a problem on the supply side where the earth is maybe breaking down?? or is my brand new all signing and dancing meggar goosed???.
And this is not flats either!!!
Thanks
Last edited: