Still trying to get to grips with new EICR coding - got 400 ohms on earth rod all protected by 30mA rcd. What would you code this as under the new EICR?
 
Code 3......it complies with the BGB in all aspects other than the recommended max of 200 ohms.....and assuming the RCD(s) operate within spec disconnection times are met.
No doubt there will be cries of anguish from some.....but the sole purpose of an EICR is to highlight deviations from BS7671,it is not permitted to bring personal preferences into coding. A code3 is nevertherless recommending improvement,and this could be explained more fully in the report summary.
 
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable​
 
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.

HOWEVER

400ohms is very low. Maybe its not in earth but sitting in a pit filled with hard core?
I would make it a Code 2 and recommend you bang in a new earth rod.
 
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.

Only while the RCD is working correctly!! lol!!

Agree with wirepuller in this instance, as this is conducting an official EICR to the current wiring regulations/BS7671.

...Not that i particularly agree with this section of them!! lol!!
 
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable​

I take your point...I've always considered this to be a roundabout way of recommending a max of 200ohms.....but you are correct,it's depends on your interpretation.
 

Reply to High Ze coding on new EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top