Still trying to get to grips with new EICR coding - got 400 ohms on earth rod all protected by 30mA rcd. What would you code this as under the new EICR?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss High Ze coding on new EICR in the UK Electrical Forum area at ElectriciansForums.net
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable​