Kevin
We've had a couple of jobs like this lately, where we have reported a high Ze reading back to the DNO. They have subsequently come and fitted a 100mA RCD between the meter and the CU.
I would have thought they would need to find the reason for the high values instead. Surely an RCD is used a supplementary protection, not primary. The job I looked at was a TNC-S system, so logically thinking, wouldn't a high Ze value possibly indicate a problem with the neutral?
Also, obviously the problem of the high Ze remains, so Zs readings may well be over the accepted limits..then how am I supposed to complete a test certificate??
many thanks
K
I would have thought they would need to find the reason for the high values instead. Surely an RCD is used a supplementary protection, not primary. The job I looked at was a TNC-S system, so logically thinking, wouldn't a high Ze value possibly indicate a problem with the neutral?
Also, obviously the problem of the high Ze remains, so Zs readings may well be over the accepted limits..then how am I supposed to complete a test certificate??
many thanks
K