High Ze - DNO added an RCD! | on ElectriciansForums

Discuss High Ze - DNO added an RCD! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

K

Kevin

We've had a couple of jobs like this lately, where we have reported a high Ze reading back to the DNO. They have subsequently come and fitted a 100mA RCD between the meter and the CU.

I would have thought they would need to find the reason for the high values instead. Surely an RCD is used a supplementary protection, not primary. The job I looked at was a TNC-S system, so logically thinking, wouldn't a high Ze value possibly indicate a problem with the neutral?

Also, obviously the problem of the high Ze remains, so Zs readings may well be over the accepted limits..then how am I supposed to complete a test certificate??

many thanks

K
 
Your Zs readings are covered by the addition of the RCD (max 500 Ohms).

I would expect the 100mA RCD to be a temporary measure in the interim while investigative work is carried out.
 
Thanks for the reply.

So you would be happy to sign a test cerificate, or a periodic if the Zs readfings were too high, as long as there was RCD protection? Or would you contact the DNO, and establish if they were coming back to rectify the problem first ?

K
 
I doubt the DNO will actually conduct any further investigation.
Your problem, will be in the future when the RCD plays up, who will be responsible for replacing the RCD?
 
On the basis of the RCD, your Zs readings will comply because your disconnection times are met by that device.

Your PIR will show how compliance was achieved.

The DNO normally use an RCD as a temporary measure when Ze is slightly above the agreed maximum.

What was Ze out of interest?
 
I doubt the DNO will actually conduct any further investigation.
Your problem, will be in the future when the RCD plays up, who will be responsible for replacing the RCD?

How is that his problem?

As long as the DNO supplied and installed device is noted on your 'comments' section then you 've done exactly what would be expected of you.
 
The one job I went to it was 1.11

My thoughts though, are that there could well be an issue with the incoming neutral, as it's TNC-S.

Not sure how we would complete an installation certificate, if one was ever required, would a comment on the existing installation suffice ?
 
Yes 'following our report of an exceeded max Ze reading, the DNO supplied and installed a 100mA RCD. Our certification was carried out with this device in place'
 
If i were you i would try to find out if your DNO are planning to come back in the near future to sort out the fault . If not i would look at it as a latent fault and swap it to a stake . It could easily be a poor neutral joint thats on the way out , depending on your bonds could be bad mojo in that house !
 
If i were you i would try to find out if your DNO are planning to come back in the near future to sort out the fault . If not i would look at it as a latent fault and swap it to a stake . It could easily be a poor neutral joint thats on the way out , depending on your bonds could be bad mojo in that house !

Could be, tenant was also complaining of power fluctuations, though no evidence of it whilst I was there of course. Have now passed it back to the DNO.
 
Sounds funny to me? After initial testing (pre board change) unless the Zs's were well within the limits i'd be thinking about walking away until the problem was solved by the DNO.

Like said though if the results are fine and you have noted the problem then it's all good.
 
It may not be a neutral problem at all, after all a PME system is just a glorified TT system. They may have problems with the stakes/spikes they had fitted, there may have been construction work further upstream that meant stakes were removed or having to be resited.

I go along with IQ here I think this is something temporary. I can not imagine the DNO just fitting an RCD and walking away. There may be a failing neutral but I bet you they are trying to find what it is and how to fix it.
 

Reply to High Ze - DNO added an RCD! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
Your biggest mistake is admitting to a mistake.... If theres no witnesses, it didn't happen. However.... A few golden rules.... Never trust...
Replies
6
Views
115

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top