I have recently re-wired a property with T-N-S earthing to find out that the Ze was 13.41ohm. I checked all the supply have to the spilt concentric incomer that looked pretty new. All connection were ok so i rang norweb. The question is does the DNO have to supply an earth to the property? An electrician i know said that the can just make to sort it yourself with an earth spike.

Cheers Paul

P'S before i left i put a 30ma RCD between the tails and the consumer unit
.
 
Last edited:
Last time i came across similar problem i called YEDL on behalf of the customer, they sent an engineer within the hour and PME'd it.

Cheers............Howard
 
The question is does the DNO have to supply an earth to the property? An electrician i know said that the can just make to sort it yourself with an earth spike.

Yep, there is a possibility that they can say that, or they could PME or fix the fault in the cable. The question has to be though, do you feel lucky?

Another question would also be how comes you didn't check the Ze before rewiring the property though, I thought that the first thing to do would be to check whether there was an adequate earth in line with reg 131.8.

But at least you've left it safe which some people wouldn't have done.... :)
 
The Supply company has no obligation to supply an earth however if an earth has been supplied, there is an obligation to maintain it.

I came upon a similar situation a few months back and the DNO were out within 2 hours and found the fault after a further 2 hours.

Ze 16.7 Ohms originally, 0.25 Ohms on completion!
 
Hi I have the same problem... on an overhead supply...T-n-c-s Ze reading of 3.5ohms?.. giving me a PFC of 62A! a good distance from the sub.stn.
will the DNO be able to do anything with this?.
 
Hi I have the same problem... on an overhead supply...T-n-c-s Ze reading of 3.5ohms?.. giving me a PFC of 62A! a good distance from the sub.stn.
will the DNO be able to do anything with this?.


If the DNO has provided you with a PME connection, they are duty bound to maintain that earth connection. And 3.5 ohms on a PME system means there is something very wrong, probably a connection problem on the overhead supply.
 
They will likely be out very quickly for a PME fault as it could be an immediate danger. Although pme faults are actually very rare.
With our lot we are still duty bound to maintain an earth were provided. This means if we can't repair we will supply 100ma time delay and plastic enclosure which is then also a handy isolator!
 
If the DNO has provided you with a PME connection, they are duty bound to maintain that earth connection. And 3.5 ohms on a PME system means there is something very wrong, probably a connection problem on the overhead supply.

Ok many thanks. All ccts are RCD protected.And RCds tested for trip times.The figure rduces when i reconnect the bonding to i/c services.However its way over the required resistance.
 

Reply to High Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top