Hello,
Doing an EICR for a storage company who share an old aircraft hanger with an engineering firm.The mains are shared and split at the main intake position by means of busbar and switch fuses which date from the 50's. The earthing system is TNS, with the mains armoured into a cast iron spreader box and the main earth off of this.
Not able to isolate the mains,I found an unused switch fuse at the mains position and carried out the Ze test.
It was performed with a Fluke multi meter (calibrated,check boxed,new leads) Earth on the earth bar, Neutral on the neutral bar and the Live across each of the phases. L1-1.10 ohms L2-1.41 ohms and L3- 1.09 ohms
Hmmm, thinks I, may have an earth fault. Contacted SSE who turn out and put a two wire test on the Ze. Neutral and earth of there meter to the earth bar and Live to each of the phases. 0.68 was there result. 'nothing wrong with that,mate'.
OK, I can replicate there two wire meter test and get the same results , however, when I try and record a Zs at a socket or light I am back with the higher values.
Why the discrepancy between the three wire and two wire Ze results?
Why does connecting the meter to neutral make such a difference?
Thanks
Dave
Doing an EICR for a storage company who share an old aircraft hanger with an engineering firm.The mains are shared and split at the main intake position by means of busbar and switch fuses which date from the 50's. The earthing system is TNS, with the mains armoured into a cast iron spreader box and the main earth off of this.
Not able to isolate the mains,I found an unused switch fuse at the mains position and carried out the Ze test.
It was performed with a Fluke multi meter (calibrated,check boxed,new leads) Earth on the earth bar, Neutral on the neutral bar and the Live across each of the phases. L1-1.10 ohms L2-1.41 ohms and L3- 1.09 ohms
Hmmm, thinks I, may have an earth fault. Contacted SSE who turn out and put a two wire test on the Ze. Neutral and earth of there meter to the earth bar and Live to each of the phases. 0.68 was there result. 'nothing wrong with that,mate'.
OK, I can replicate there two wire meter test and get the same results , however, when I try and record a Zs at a socket or light I am back with the higher values.
Why the discrepancy between the three wire and two wire Ze results?
Why does connecting the meter to neutral make such a difference?
Thanks
Dave