High looking for a bit of advice might be picking this up incorrect.
A main supply panel board with an 800a and 400a mccb feeding a factory an office block respectively.
Tested Ze 0.07 ohms
Production Building Zs 0.04 ohms
Office Block Zs 0.07 ohms
Length of runs from panel board to both buildings are 130m and are both bonded down to the steelwork.
The max permitted Zs reading for an 800a mccb is 0.028.

How are you meant to achieve readings as low as 0.028 with a Ze of 0.07 ohms or as i say am i reading this wrong.
Any help would be gratefully received.
 
with a supply of 800A, you woul;d usually have a transformer nearby, and as such your Ze should be very low. I would ring the DNO. It does sound high for a supply of that size.
 
High looking for a bit of advice might be picking this up incorrect.
A main supply panel board with an 800a and 400a mccb feeding a factory an office block respectively.
Tested Ze 0.07 ohms
Production Building Zs 0.04 ohms
Office Block Zs 0.07 ohms
Length of runs from panel board to both buildings are 130m and are both bonded down to the steelwork.
The max permitted Zs reading for an 800a mccb is 0.028.

How are you meant to achieve readings as low as 0.028 with a Ze of 0.07 ohms or as i say am i reading this wrong.
Any help would be gratefully received.

Just out of interest, where did you get your max Zs requirement for the 800 MCCB??
 
Talpult also if your using a bog standard MFT then you starting to go down the scale to a point where your not going to get a decent results because the lack of resolution at this level.

There is a great sticky on here by IQ on how you can combat these low value levels using a wander lead, which might give you a more accurate Ze, Zs readings.

also as E54 was that 0.028 the manufacturers value
 
The transformer is 5m away form the main panel board.The supplier provided a 3 phase and neutral supply and we were instructed to link out the neutral and earth terminals within the panel board by the supplier which was done .Obviously giving us a tncs system
There is an acb main switch rated at 1000 amp feeding the the 800 and 400 amp mccbs.
The switchgear is abb and we contacted the panel board manufacturer who sent us the max zs readings.
thanks for you guys input.
 
It will be TN-S unless the DNO have linked the neutral at the transformer. In which case they wouldn’t have asked you to link N-E, they would have provided the earth.
 
As Tony has quite correctly pointed out, your N-E connection is the transformers Neutral being earthed. This is quite a normal practice on a dedicated DNO supplied transformer supply. So if you are experiencing high Ze values you can add extra earth rods to the transformers grounding ring. You really should be aiming for less than 10 ohms, obviously, the lower you can get your Ra values the better will be your final Ze value.

As a matter of interest, what size is the TX, and what sort of transformer protection do you have on your main switchboard??
 

Reply to High Zs on 800A MCCB in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
379

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top