graham123

Testing a new terrapin buliding at a primary school today. The supply to the terapin is 90metres of 35mm 4core. Swa as CPC. At the terapin db i get 0.59 ohms as Zs. All the circuits in the terapin are 30ma RCD protected. Is this acceptable as the zs of the individual circuits does not meet the disconnection times of the RBCO. I heard somwere that if the circuit was 30ma rcd protected Max zs did not matter. Thanks Graham
 
with RCD, max. Zs is 1667 ohms ( 30mA RCD . the |RCD will then act aS FAult protection .
 
so RCBO is protecting a circuit which has high ZS but is below 1667 ohms so thats covered by that and then we have to have RCD tests below 20mseconds for TN systems and 7mseconds for TT system at 1x test. Is this correct??
 
Ha,ha!!!! And once again, bang goes the ''Additional protection'' status on a TN system, as the additional protection has now become your primary protection, ...and before the installation is even put in to service What's more it's an electronic means of protection, that can go belly up at any time.

The fact is, that your 35mm cable can't and/or isn't delivering a suitable means for ADS operation, so it doesn't conform.
Bit different if you lost a working ADS due to a loose connection or whatever during service, but on a new installation?? As a customer, i'd expect everything about that new installation to be A1, not fundamentally flawed from the very start....

I really don't know why you guy's even bother checking circuit Zs any more, as your never going to exceed 1667 ohms!!!
 
Last edited by a moderator:
If you are intending on relying on RCBO's I Would at least do a loop test from L-N at each of the circuits though, as it may be a dodgy live connection giving the high readings and under short circuit conditions may not operate the RCBO's.
 
I'm definately with E54 in his view on this issue.
Why bother with earthing at all if your just gonna rely on rcd's , just smacks of poor design IMO.
The dustbin in my back yard probably has an earth reading below 1667 lol.
 
Also agree with Eng and Biff here. Can't add any more than they have. Why design a system properly when you can just pop in a "magic RCD" and all your worries float away....
 
I would have thought that a Zdb of 0.59 ohms was sufficient for the type of circuits run in a terrapin.
What circuits are installed?
half a dozen sockets, half a dozen lights, a couple of panel heaters?
Why not use 16A radials for the power circuits that will increase your minimum allowable Zs....
 

Reply to high zs reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
386
Yes, probably overthinkig, thanks.
Replies
6
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top