J

justuk68

Guys, request advice.

I was recently carrying out remedial work on 2x Ltg cts reported on EICR as having very high Zs value.

When I retested the measured Zs was 44.8 and 42.6. These are on a TNC-S system and Crabtree C50 5a MCBs. These would appear to be readings expected of a TT System!

I repaired CPC connections and carried out good R2 tests at all the fittings. There was also good 240v at the fittings L-CPC.

My tester is in Date for cal and I have no reason tho suspect it to be at fault. Check test on x2 other circuits on same DB were OK. I did not use the Trip Lock function on the tester. I do not expect the Zs at the DB to be high as nothing else was reported to be high on the EICR.

Could an old MCB be the cause, loose MCB or connections??

Your thoughts please............
 
Step 1 test Zdb
Step 2 test R1 + R2, R1 + Rn and R2 + Rn
Step 3 calculate expected Zs
Step 4 measure Zs
Step 5 if everything above apart from step 4 is ok measure resistance / impedance across mcb.
 
Gents Thanks,

Highest R2 was .84
Did not measure Ze as I did't suspect it to be high (EICR no mention, and my check tests)

The DB is 25yrs ish and like a birds nest. ID of 'N' and 'CPC' very difficult. Given the tests I've carried out just wondered what you Guys think???........
thanks
 
Last edited by a moderator:
Gents Thanks,

Highest R2 was .84
Did not measure Ze as I did't suspect it to be high (EICR no mention, and my check tests)

The DB is 25yrs isn and like a birds nest. ID of 'N' and 'CPC' very difficult. Given the tests I've carried out just wondered what you Guys think???........
thanks

I would say it's defo worth getting a Ze and some other Zs reading off local circuits and go from there ?
 
Gents,

Totally get the not taking things for granted comment.

Im fairly competent testing but not seen this type of fault given all my CPC checks etc.

Think when I return I will initially check the MCB connections retest, then try the Alt MCB!

Thanks again.....will let you know result........
 
One of the first things that should be done is to carry out a Ze as soul man has said you could have a high Ze which will effect the zs , to carry out the Ze you should isolate the supply and disconnect the main earth and test connected to the disconnected earth and the incoming L and N , this eliminates parallel earth paths from the circuits , you could have a high Zs due to a fault on the incoming earth or the earth connected to an un connected earth block on the side of the cut out and its using parallel earth paths ,
 

Reply to High Zs reading! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
603
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
399

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top