Guys, request advice.
I was recently carrying out remedial work on 2x Ltg cts reported on EICR as having very high Zs value.
When I retested the measured Zs was 44.8 and 42.6. These are on a TNC-S system and Crabtree C50 5a MCBs. These would appear to be readings expected of a TT System!
I repaired CPC connections and carried out good R2 tests at all the fittings. There was also good 240v at the fittings L-CPC.
My tester is in Date for cal and I have no reason tho suspect it to be at fault. Check test on x2 other circuits on same DB were OK. I did not use the Trip Lock function on the tester. I do not expect the Zs at the DB to be high as nothing else was reported to be high on the EICR.
Could an old MCB be the cause, loose MCB or connections??
Your thoughts please............