what causes high zs readings on a ring socket circuit and when testing end to end l=0.60 n=0.68 e=over 200 help what could this be
 
Sounds like you have a poor connection on the cpc. It will quite likely be a poor termination in an accessory or worste case a damaged cable.
 
what causes high zs readings on a ring socket circuit and when testing end to end l=0.60 n=0.68 e=over 200 help what could this be

The advice already given is a good place to start.
TBH, without meaning to offend, but if I had to ask questions as basic as this then I would cease testing till I was more competent to dictate and assess measured values.
 
thanks for the reply and comments however we all need a liitle advice now and again my thinking was also loose cpc but having only replaced consumer unit and not doing a full periodic how far do u go and surley loose cpc would not such a high r1+r2 could it be that the ring is cross connected with the other ring as other ring was not giving continuity on e-e but did on r1+r2
 
thanks for the reply and comments however we all need a liitle advice now and again my thinking was also loose cpc but having only replaced consumer unit and not doing a full periodic how far do u go and surley loose cpc would not such a high r1+r2 could it be that the ring is cross connected with the other ring as other ring was not giving continuity on e-e but did on r1+r2

A loose cpc connection could give you a number of readings, just depends how loose it is.

You need to 'break' the circuit down and locate where this 'fault' is.

I would suggest to your client that some investigation and fault finding is required on the installation.
 
I have not read through all the responses so this may have been offered already, end to end and indeed rfc tests are only part of Xs , the proof needs Ze to be measured b4 u start pulling the installation apart
 
his r2 reading is 200 ohms, so it's got to be a fault on the circuit. wander lead , test fom one end of cpc in CU from socket to socket, till the reading jumps.
 
Last edited:
thanks trebor have done a ze is very good reading 0.08 on tn-s replaced consumer unit cpc impeadence readings are rubbish on both rings one ring no reading end to end other ring high reading end to end and high r1+r2 and loops high aswell i think i tell customer more investigation need to cover myself on installation certificate though
 

Reply to high zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
600
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top