High Zs readings | on ElectriciansForums

Discuss High Zs readings in the UK Electrical Forum area at ElectriciansForums.net

M

markc17

Hi all, some advise please...
I have a building full of type 4 3871 FE breakers, that have recently undergone a PIR. Many of the ring circuits have come back as having high Zs readings and have thus failed, with each only failing by like 0.04 of an ohm. There are no earths in the circuits, with the conduit and trunking system being used. Without going into reasons why, it is unlikely i am going to be granted the time or resources to pull new earth wires down to each of the affected circuits. Was just wondering my options... I have managed to procure some 30ma Federal Electric RCBO's off Ebay, and was wondering if by fitting these it would mean my readings would comply? Ill be honest, im a bit confused by the 1,667 ohm allowance on a 30ms rcd. Any clarification would be greatly recieved.
Just so you know, i cannot gain access to alot of the conduit system, so am unable to tighten much, i could possibly increase some of the bonding?
Thanks, Mark
 
Hi all, some advise please...
I have managed to procure some 30ma Federal Electric RCBO's off Ebay, and was wondering if by fitting these it would mean my readings would comply? Ill be honest, im a bit confused by the 1,667 ohm allowance on a 30mA rcd. Any clarification would be greatly received.

The 1667 ohm is just the Ra x Idn <=50v so with a current of 0.03A and 50 V resitance (Zs0 must be less than 1667 ohms.
This is a way of overcoming the issue but relies in the RCD, however you would still disconnect the breaker just not in the required time.
 
The use of and RCD/RCBO is one way around your problem, but as already said, it would be a better job to try and find why your readings appear high.

Its all to easy to say bang in a RCBO and be done IMO
 
Federal Electric breakers, I take it, these are those black Bakelite ones?? ...I wouldn't give you tuppence for them!!
These should be treated the same as the old VOELB's, with a recommendation to replace!! lol!!
 
Thanks all... basically its a building that is in constant use, to upgrade main earthing and the like is, at the moment atleast, an impossibility. All readings at the intake etc, fall within regs, and the high Zs readings i am getting fall within the regs in BS7671, but are outside the rule of thumb readings in the OSG..... when i say outside i mean literally by a few points of an ohm... still got a code 2 tho. Am assuming that its the path of the conduit and trunking that is the issue.. to pull into the rooms that are an issue is again fairly difficult to do at the moment so was just wondering about adding extra bonding to the conduits, or trunking.. and whether this would be seen as bead practice or acceptable? I would like to get the readings under if poss, rather than juhst add an rcd...
thanks again guys
mark
 

Reply to High Zs readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
597
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
867

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top