T
thekingiam
First of all readings from kitchen ring circuit are as i remember insulation resistance all well above 2 meg now!problem i had was extension had flat roof and cable was damaged between two points replaced damaged cable but still mcb not rcd as they aint got one is breaking.this was when no load present and thought rectified well it lasted 3 days then phone call that it had tripped again went back today took a couple of readings before forced out on other job what i took was zs readings from all sockets and got average 0.34 then a reading at replaced cable socket say socket A of 47 ohms tried reading at connecting socket say socket B in ring and got 46 ohms, disconnected new earth from first socket A and A read at 0.45 and B read at 347 ohms read all sockets and they were still normal.
so i have deduced that a bad earth connection from socket B to a socket before and will test continuity on sunday but my main question is how a large zs can cause an overload to trip mcb?
or after solving this problem should i look further?
so i have deduced that a bad earth connection from socket B to a socket before and will test continuity on sunday but my main question is how a large zs can cause an overload to trip mcb?
or after solving this problem should i look further?