Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
 
Theres 2 rings in the bungalow. One for the kitchen and one for the rest of the house Kitchen readings were r1 0.49 rN 0.49 r2 0.83. So even these figures seem a bit high then? MFT has been calibrated recently and checked it against my Cal card the other day.
 
Theres 2 rings in the bungalow. One for the kitchen and one for the rest of the house Kitchen readings were r1 0.49 rN 0.49 r2 0.83. So even these figures seem a bit high then? MFT has been calibrated recently and checked it against my Cal card the other day.
If you are measuring the rfc loop e2e and it's made from 2.5 /1.5 then these seem ok to me as 0.49x2.5/1.5 = 0.817, so practical reading of 0.83 gets a tick :)
This would indicate an rfc about 65m length end to end and added to your Ze 0.14 should give Zs of around 0.47 ish which is fine for 32A. Is that roughly the Zs you've measured?
 
If you are measuring the rfc loop e2e and it's made from 2.5 /1.5 then these seem ok to me as 0.49x2.5/1.5 = 0.817, so practical reading of 0.83 gets a tick :)
This would indicate an rfc about 65m length end to end and added to your Ze 0.14 should give Zs of around 0.47 ish which is fine for 32A. Is that roughly the Zs you've measured?
Yep, 0.46 was my highest value in the kitchen. My calcs work out for the other ring (apart Zs sockets) work out, but r1 r2 & rN values are high if you put them against cable resistance table in GN3. See post 12 for other values.
 
The socket with the highest reading had 2 x 2.5 T&E. Took L-L, N-N, E-E reading at the consumer unit. r1 + r2/4 + Ze = 0.82 Ze was measured at 0.14. The calculated Zs of 0.82 was very near what i was getting all around the ring. 2 sockets were a bit lower (0.45 & 0.55) and apart from the 2 that were high, the rest were virtually spot on. ( My end to end values were L=0.92 N=0.92 E=1.83)
Td to end is a bit higher than expected calculation of 1.55 this may be down to loose/bad connection or 1.0mm cpc(or in part of) that aside did you do a R1 +R2 dead test this will prove that these two sockets are spurs. Midwest posted a good point in post #21 put the ends together at the C.U. and do a ring test at the high reading socket will prove it. You posted that there was still two cables at the highest reading socket my feeling is that there is another socket/outlet from this you have not located maybe in loft just a thought. Let us know what you find out on Monday
 
Td to end is a bit higher than expected calculation of 1.55 this may be down to loose/bad connection or 1.0mm cpc(or in part of) that aside did you do a R1 +R2 dead test this will prove that these two sockets are spurs. Midwest posted a good point in post #21 put the ends together at the C.U. and do a ring test at the high reading socket will prove it. You posted that there was still two cables at the highest reading socket my feeling is that there is another socket/outlet from this you have not located maybe in loft just a thought. Let us know what you find out on Monday
I hope its not in the loft, its covered in insulation. Two layers, And there's hardly any space to move....:rage:
 
Im still scratching my head a bit as to why my r1 rn r2 values on the offending ring are as high as they are. The circuit cant be over 120m, so why so high?? ultimately if the Zs ok then its not a problem. Unfortunately my brain doesnt work like that and i always what to know why things are what they are!! Bit OCD!
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top