Was having this discussion today with the guy i was working with.

You went and did an PIR and found several of the ZS current over the max ZS alloud by the regs so wont disconnect in 0.4s. I was told on the 2392 tesing course that it would be okay to put these circuits on an rcd, as this will allow the circuit to disconnect within 0.4s. what do you think of this practise. Personnally i dont agree with it nor did the guy i was working with.
 
This type of question comes up on 2392/91 question papers from time to time where it tells you the measured Zs for a particular circuit exceeds the maximum permitted in BS 7671 and to state 3 ways of combating this

1. Downsize the protective device
2. Increase the size of CPC
3. Install additional RCD protection.

So, installing additional RCD protection whilst it may be seen as a 'quick fix' is an acceptable solution, for remedial works after a PIR anyway. If it were a new install I would be thoroughly inspecting & testing the circuit as IMO there is no reason for the Zs values not to be met, unless it's a TT install of course.
 
Was having this discussion today with the guy i was working with.

You went and did an PIR and found several of the ZS current over the max ZS alloud by the regs so wont disconnect in 0.4s. I was told on the 2392 tesing course that it would be okay to put these circuits on an rcd, as this will allow the circuit to disconnect within 0.4s. what do you think of this practise. Personnally i dont agree with it nor did the guy i was working with.

Classic BS7671 again. Tells you one thing, then tells you something else. I would also want to bottom the original problem. Just fitting a RCD cures the symptoms but not the disease so to speak.

Cheers..............Howard
 
It would depend on the reasons why the Zs exceeds the max for the overcurrent device. It may be that a type C has been fitted to a circuit to allow for equipment with a high inrush current,when the measured Zs would be OK with a type B. This is simply because of a change of overcurrent device and not a design or other problem. IMO in such circumstances it would be acceptable to rely on an RCD to meet disconnection times.
 
I agree with this but over time the max zs values have been lowered with amendments to the regs. So a once acceptable ZS reading may no longer be, so providing you have evidence of this through past test results then i would only put the circuit on an rcd. Another thing some where in the regs it states that an RCD shouldn't be the sole protection of the circuit.
 
I agree with this but over time the max zs values have been lowered with amendments to the regs. So a once acceptable ZS reading may no longer be, so providing you have evidence of this through past test results then i would only put the circuit on an rcd. Another thing some where in the regs it states that an RCD shouldn't be the sole protection of the circuit.


That is referring to overcurrent protection,there is no reason why an RCD cannot be the sole means of earth fault protection.

edit-(Lenny types quicker than me!)
 
Last edited by a moderator:

Reply to high ZS what would you do? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top