Hi folks
Just tested a convent/nursing home for nuns

found some long ring circuits frotected by 32A Type C RCBOs, the max Zs allowable is 0.72, but i was getting readings between 0.83 and 0.98.

Are these readings acceptable because of the use of RCBOs, i.e. does it matter what the reading is as an RCBO is likely to trip during a fault regardless

Or should a type B RCBO be fitted?

Note: its a TN-C-S system

thanks
 
No, disagree, fit the right one like spin says. Circuit should comply at dead test level even when its a TT so as long as can get one a type B then larfin'.

Rcd might fail (yes i know this is an rcbo) and then what. Crap resistance and an MCB thats not keen....
 
agree with spinlondon. but just a thought.... if possible, measure R1+R2. it has been known for RCBOs and RCDs to inflate the Zs readings due to their internal components.
 
or poor design. was said that it was a long circuit, so maybe should have been wired in 4mm. that or should have used type B . it's not known why type C have been fitted. could have been just what was in stock needed using.
 
To my mind yes.
RCDs are additional protection....RCD's can also provide earth fault protection.411.5.2....411.4.9...,RCD's for additional protection only cover some equipment listed in 411.3.3
What you have here is a device which should provide both overcurrent and earth fault protection, it would seem to me a bit pointless using such a multipurpose device, if it does not do the job it is designed to do.It does provide both overcurrent and earth fault protection,overcurrent can be due to short circuit,not just earth fault[/QUOTE]


Rcd's also provide earth fault protection.....if they didnt a TT system would not be practical.....there is also a requirement for fault (short circuit)protection which a typeC overcurrent device will provide instantaneously,therefore it is not pointless. In this instance with the Zs 0f 0.98 a 32a type C will take approximately 8 seconds to disconnect an earth fault without the RCD,so even if the RCD fails a type C is not a complete waste of time.The Rcd will meet the disconnection times for earth fault protection.
I think if this is a result of a PIR it may be hard to justify the expense to the client of replacing RCBO's which already comply with the regulations,and provide satisfactory protection,based on a personal opinion,rather than a regulation.
 
Last edited by a moderator:

Reply to High Zs with RCBO in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top