Hi folks
Just tested a convent/nursing home for nuns
found some long ring circuits frotected by 32A Type C RCBOs, the max Zs allowable is 0.72, but i was getting readings between 0.83 and 0.98.
Are these readings acceptable because of the use of RCBOs, i.e. does it matter what the reading is as an RCBO is likely to trip during a fault regardless
Or should a type B RCBO be fitted?
Note: its a TN-C-S system
thanks