13amp FCU off ring main supplying sockets in shed.
Zs at furthest socket in shed is 1.26ohms which is too high for a 32 amp mcb.
Would you use the 13amp fuse in the FCU to meet your Zs reading?
Zs at FCU is 0.70.
I understand your logic i.e. what's the difference between have a socket with a 13A extension reel going into vs a FCU with 13A fuse and long "extension" out to garage.
However difference is fixed vs non-fixed wiring. For fixed wiring then I think you already know the answer. So I would personally be looking to (depending on cost and longer term plans):
1. increase size of cable from FCU to sockets in garage, to reduce Zs to within acceptable limits.
2. or run a separate circuit for the CU to the garage with acceptable Zs for that circuit.
I know it's not ideal, but keeps you right.
Cheers @davesparks Guess I'm belt and braces type of guy. Always thinking worst case and looking at potential changes down the line....It is protected by the 13A fuse so needs to meet the Zs requirement for the 13A fuse.
[automerge]1592384713[/automerge]
It is protected by the 13A fuse so it is fully compliant and nothing needs to be done.
Agree with you fullyWhat worst case are you looking at here?
And what potential change?
We cannot protect against potential changes down the line because we cannot know for certain what will, or will not happen in the future.
Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.
Has RCD protection as well.
Most answers confirming what I thought with it being ok but have heard mixed opinions on this before.