13amp FCU off ring main supplying sockets in shed.
Zs at furthest socket in shed is 1.26ohms which is too high for a 32 amp mcb.
Would you use the 13amp fuse in the FCU to meet your Zs reading?
Zs at FCU is 0.70.
 
I understand your logic i.e. what's the difference between have a socket with a 13A extension reel going into vs a FCU with 13A fuse and long "extension" out to garage.

However difference is fixed vs non-fixed wiring. For fixed wiring then I think you already know the answer. So I would personally be looking to (depending on cost and longer term plans):

1. increase size of cable from FCU to sockets in garage, to reduce Zs to within acceptable limits.
2. or run a separate circuit for the CU to the garage with acceptable Zs for that circuit.

I know it's not ideal, but keeps you right.
 
I am not sure what you are saying

Is it you have a rfc with a fcu, the ring maximum Zs is lower than its protective device 32A mcb - so 1.1 ohm.

Then you have a sub circuit from this fcu this circuit has a lower Zs than its protective device 13A fuse - so 1.84 ohm.

Where is the high Zs related to?
 
13amp FCU off ring main supplying sockets in shed.
Zs at furthest socket in shed is 1.26ohms which is too high for a 32 amp mcb.
Would you use the 13amp fuse in the FCU to meet your Zs reading?
Zs at FCU is 0.70.

It is protected by the 13A fuse so needs to meet the Zs requirement for the 13A fuse.
[automerge]1592384713[/automerge]
I understand your logic i.e. what's the difference between have a socket with a 13A extension reel going into vs a FCU with 13A fuse and long "extension" out to garage.

However difference is fixed vs non-fixed wiring. For fixed wiring then I think you already know the answer. So I would personally be looking to (depending on cost and longer term plans):

1. increase size of cable from FCU to sockets in garage, to reduce Zs to within acceptable limits.
2. or run a separate circuit for the CU to the garage with acceptable Zs for that circuit.

I know it's not ideal, but keeps you right.

It is protected by the 13A fuse so it is fully compliant and nothing needs to be done.
 
It is protected by the 13A fuse so needs to meet the Zs requirement for the 13A fuse.
[automerge]1592384713[/automerge]


It is protected by the 13A fuse so it is fully compliant and nothing needs to be done.
Cheers @davesparks Guess I'm belt and braces type of guy. :oops:Always thinking worst case and looking at potential changes down the line....
 
What worst case are you looking at here?
And what potential change?

We cannot protect against potential changes down the line because we cannot know for certain what will, or will not happen in the future.
Agree with you fully :)

Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.

No matter what we try to protect against (perceived or real) something will always be missed, hence evolution of the regs over the years.

Hope that makes sense? Apologies if I've inadvertently offend you, certainly was not my intention.
 
Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.

Whilst those things can and do happen it is still very hard to protect against them now, and certainly unfair to charge a customer for extra work to protect against something they, or a future owner of a property might do.
 

Reply to High Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
375
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
943
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi, it turned out to be a very corroded socket outlet, and not a ring. It was two radials. An EICR had been carried out.
Replies
7
Views
1K
  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
531

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top